WHAT IS DIFFERENCE BETWEEN TWO WIRE RTD AND THREE WIRE RTD?
Answers were Sorted based on User's Feedback
Answer / moumita
The simplest resistance thermometer configuration uses two
wires. It is only used when high accuracy is not required as
the resistance of the connecting wires is always included
with that of the sensor leading to errors in the signal.
Using this configuration you will be able to use 100 meters
of cable. This applies equally to balanced bridge and fixed
bridge system.
In order to minimize the effects of the lead resistances a
three wire configuration can be used. Using this method the
two leads to the sensor are on adjoining arms, there is a
lead resistance in each arm of the bridge and therefore the
lead resistance is cancelled out.
| Is This Answer Correct ? | 75 Yes | 8 No |
Answer / varun krishna.m kottayam
Serious lead-wire resistance errors can occur when using a
two-wire RTD (see Fig. 3A), especially in a 100Ω sensor. In
a two-wire circuit, a current is passed through the sensor.
As the temperature of the sensor increases, the resistance
increases. This increase in resistance will be detected by
an increase in the voltage (V = I•R). The actual resistance
causing the voltage increase is the total resistance of the
sensor and the resistance introduced by the lead wires. As
long as the lead wire resistance remains constant, it can be
offset and not affect the temperature measurement. The wire
resistance will change with temperature, however, so as the
ambient conditions change, the wire resistance will also
change, introducing errors.
If the wire is very long, this source of error could be
significant. Two-wire RTDs are typically used only with very
short lead wires, or with a 1000Ω element.
In a 3-wire there are three leads coming from the RTD
instead of two. L1 and L3 carry the measuring current, while
L2 acts only as a potential lead. Ideally, the resistances
of L1 and L3 are perfectly matched and therefore canceled.
The resistance in R3 is equal to the resistance of the
sensor Rt at a given temperature—usually the begining of the
temperature range. At this point, V out = zero. As the
temperature of the sensor increases, the resistance of the
sensor increases, causing the resistance to be out of
balance and indicated at V out. Resistances L1 and L3 in
leads up to tens of feet long usually match well enough for
100 ohm three-wire RTDs. The worst case is resistance offset
equal to 10% of single-lead resistance.
The optimum form of connection for RTDs is a four-wire
circuit (see Fig. 3C). It removes the error caused by
mismatched resistance of the lead wires. A constant current
is passed through L1 and L4; L2 and L3 measure the voltage
drop across the RTD. With a constant current, the voltage is
strictly a function of the resistance and a true measurement
is achieved. This design is slightly more expensive than two
or three-wire configurations, but is the best choice when a
high degree of accuracy is required.
| Is This Answer Correct ? | 35 Yes | 8 No |
Answer / yugesh shah
Commonly 2 wire rtd used wher the place rtd installed and control room where indicated the temperature is not so far
But where indicator and rtd is in distance the third wire which is known a s compensation wire is used to stop of the effect of temperature which is in atmosphere and in process area...so if u wanna exactly temperature then should use 3 wire rtd
| Is This Answer Correct ? | 2 Yes | 0 No |
The temperature indication does not increase so
significantly that it is worth the effort to use a 3 or 4
wire RTD. It might increase with something like 0,001Deg C
so that is so small you might as well say there is no
difference in the accuracy of a 2,3 and 4 wire RTD, using a
local or smart transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck
| Is This Answer Correct ? | 5 Yes | 7 No |
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)
how we will install a positioner ?
why is honed type flow orifice plate? what purpose it used? how to select this?
Instrumentation Safe Guarding test. How to determine the interval time of the test. eg:Halfyearly,Every year,Every three years etc.
I WANT TO KNOW SOME BASIC CONCEPTS RELATED TO INSTRUMENTATION
Can anyone say that formula of Converting the Diff. Pressure into Flow in Kg/Cm2 or any explaniation of Orifice Plate, Beta Ratio , How to calculate
in yokogawa prosef rd safety PLC how to data send frome local SCS to other SCS and other FCS
Sir, I want junior executive, Instrumentation question papaer for IOCL, Plz send to arabinda.ghosh83@gmail.com
pressure switch range 0 to 2bar.i have to install from ground level to 5 meters height.what is the formula the to increse the range ? and every 1 meter how much pressure should be add ?
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?
if I did short to both AO connections, channel will burn or what? m sure in AI it will damage to channel. But what will happens in AO?
CAN YOU USE MOVING COIL METER FOR MEASURING A.C?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)