steam drum level transmitter calibration procedure? with
example?
Answer / saif chowdhury
Steam Drum Level Xmt Basically Known as a Wet leg Transmeter. when steam drum Actual level is zero The Transmitter output will be Maximum i.e 20MA.
Calibration procedure:
Normally the range will be very minor in negative MMH20 Or Milibar. Because LO Side tube hold higher pressure than HI Side.
1. Isolate the Both Tapping Point (by operator)
2. Ensure Do not drain the impules tube which is filled water. Because txr zero will shift which will affect proper reading. only for flushing pupose you can drain if the impuls line is pluged then you have to refill the water and make zero again.
3. To calibrate the transmitter close both isolation valve txr manifold.
4. Prepare the 5 steps Calibration Input range.
5. apply the pressure by the vacum pump.
6. After complete the calibration check both condensate pot if filled with water till the neck or water level is proportion the exact tapping point.
7. open isolation Txr Isolation valve from manifold check txr. reading is zero.
8 then proceed to commission the both tapping point block valve or Isolation Valve.
Hope this answer to your question. Good luck !
Is This Answer Correct ? | 0 Yes | 2 No |
why we use sensing type(NPN)on a vibration monitring system not a (PNP)sensing type
Qatar fertilizer call me for interview as Instrumentation Project Engineer. Please let me know what kind of question they asked ? ALso they said they will take Written test, any idea about this written test ?
how does pressure is converted into milli amps in pressure transmitter? plzzz explain practically
What are the uses of orifice plates?
what is the daily job of an instrument commissioning supervisor
Q1: Consider part of a control loop, which excludes the transmitter, consisting of a process, a controller and a control valve which may be represented by two dead times of 0.5 min each and three exponential lags of 0.8 min., 1.0 min. and 1.5 min. respectively. We wish to express this system as an overall first order plus dead time (FOPLD) model ie gain, time constant and process dead time. (We will see later that this is often done, to simplify controller tuning). For this exercise, gain is considered to be 1.0. (A) If the transmitter is a flow transmitter whose behaviour can be described by a dead time of 0.2 min. and an exponential lag of 0.5 min. in terms of the overall dead time and overall first order lag how can the system behaviour be approximated ? Overall dead time = Overall time constant = (B) If the transmitter is a temperature transmitter with a temperature sensor in a protecting well whose behaviour can be described by a dead time of 0.7 min. and an exponential lag of 15 min. how can the overall system behaviour be approximated now? Overall dead time = Overall time constant =
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
how to turbine speed measurement?
0 Answers Jindal Steel and Power,
how to work static pressure sensore how to work dpt
What is the out put of pressure switch & electronic pressure transmitter.
5 Answers ADMA OPCO, Al-Barrak,
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
Hello to all....I am an Instrumentation Graduate and i am passed out in this year only.. I am unable to find the job in my core instrumentation.. so any boby tell me how to and where to search the job....please...and also tell me i there are any courses offered in the instrumentation stream so i can do it... you can send your suggestions to my mail-id i.e Ganesh20084u@gmail.com ... please..