How can I map a tank?
Tank 15m h and 42m dia.
we just fixed radar type lit.
its reading shows over range.
Now its required mapping ?
Answer / gp
Radar LT measure the distance, so two options to map,
one is Empty mapping of tank and other is the partial mapping of the tank level. The second option is useful while you are sure the liquid level in the tank
| Is This Answer Correct ? | 0 Yes | 0 No |
Difference between 2-Valve Manifolds, 3-Valve Manifolds and 5-Valve Manifolds 3 with diagram
How can a d.p. Transmitter be calibrated?
what is the difference between sensor and tranducers?
Please send me the sample question of Instrumentation of hpcl/iocl exam. my mail id hihi_kiholo@rediffmail.com
Why 4mA-20mA current loop selected as standard ???
How digital input and digital output 's are working in dcs
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
How to convert milliampares into flow??
Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Close on Fall Pressure Switch contacts are used. 2.If Pressure is abnormal as per set pressure,if connecting Terminal of pressure switch breaks,how the voltage extends to Relay base. 3.Are these contacts come under fail safe philasaphy.
what is plc communication?
if we mount flow tube in arrow direction then flow comes in negative & if we mount it another direction then flow comes positive,So what will be the problem
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)