My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
Answer / carl_ellis
Any 2 wire, loop powered 4-20mA transmitter that puts out
30mA is broken. The only transmitter that puts out 30mA is
a legacy 10-50mA transmitter from 20-30 years ago.
While the upper end of the 4-20mA signal range is 20.0mA,
most 2 wire, loop powered transmitters allow for some slight
signal over-range, typically 20.5mA.
NAMUR standards use 21.0 mA to signal a fault or failure
mode. Other vendors use other values, 20.8mA, 21.2mA or
some value in the range of 21mA. But no vendor uses 30mA
as a fault mode.
The transmitter is broken or dysfunctional.
Carl Ellis
Measure First
Is This Answer Correct ? | 5 Yes | 0 No |
what are the following documents comes under loopchecking
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
how many types of thermocouple cable are? give the name of each type.
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
Explain, and give a real-world example of MODULATING control
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
what is difference between total flow and flow rate in general ?? explain it with daily life example.
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
Difference between ultra sonic flow meter
what is the difference betwwen the 2wire level transmitter and 4wire level transmitter??and their applications also??
What is meant by cold float of compressor shaft.
while stroke checking of a linear control valve ,found its travel is in non linear ,what can be possible reason ? ( please answer send in mannanali65@gmail.com) pls pls pls if any body know