what is the breakdown voltage value in BDV test in
transformers?
Answers were Sorted based on User's Feedback
Answer / sudhansu kumar dalei
The BDV of oil in transformer is 60 KV/1 min within the gap
of 2.5mm in the test vessel of oil test kit.
Is This Answer Correct ? | 77 Yes | 10 No |
Answer / rajesh kumar.k
As per IE rule it should withstand 40kv/min.
Is This Answer Correct ? | 39 Yes | 12 No |
Answer / yog111283
as per rule. after oil filteration oil sparking value must
be more than or at list 60 kv
Is This Answer Correct ? | 30 Yes | 12 No |
Answer / kishore
the minimum aceptable value of breakdown voltage in BDV
test is >30KV
Is This Answer Correct ? | 15 Yes | 6 No |
Answer / nitin arora
It depends on the voltage rating of the transformer
IF transformer rating is less than 72 KV then minimum BDV should be 30 KV.
IF transformer rating is 72 to 170 KV then minimum BDV should be 40 KV.
IF transformer rating is more than 170 KV then minimum BDV should be 50 KV.
All above results are referring the 2.5 MM gap during test.
Is This Answer Correct ? | 6 Yes | 0 No |
For veryfication of oil purity every year to be checked the
BDV(breakdown voltage),we have take out the transformer
oil in the transformer and collect in the high voltage kit
inthe kit two stem will be there within the 2mm gap and
then apply the high voltage 50kv for 1 minute and it
shiould be withstand upto the mentioned time.Otherwise oil
to be filtered.
Is This Answer Correct ? | 24 Yes | 38 No |
what the main difference of the 3 phase and 2 phase power supply??
how to select rating of HT Panel
What is Earthing?
how we calculate the 30 KW 3phase electric motor current on noload
23 Answers Monnet, Siemens, SSR, Supermac Industries,
what will happen if the bus PT fuses are accidently removed from the circuit in 6.6kV feeder?
What is APFC Panel????
Main Differance between Primary Distribution & Secondary Distribution Of Electricity....?
what is b checks and m checks in diesel generator maintenance?
what does the word synchronous mean in 'synchronous machine'
Which motor connection is preferable star-delta or delta-star?
Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?