what is the breakdown voltage value in BDV test in
transformers?
Answers were Sorted based on User's Feedback
Answer / sudhansu kumar dalei
The BDV of oil in transformer is 60 KV/1 min within the gap
of 2.5mm in the test vessel of oil test kit.
Is This Answer Correct ? | 77 Yes | 10 No |
Answer / rajesh kumar.k
As per IE rule it should withstand 40kv/min.
Is This Answer Correct ? | 39 Yes | 12 No |
Answer / yog111283
as per rule. after oil filteration oil sparking value must
be more than or at list 60 kv
Is This Answer Correct ? | 30 Yes | 12 No |
Answer / kishore
the minimum aceptable value of breakdown voltage in BDV
test is >30KV
Is This Answer Correct ? | 15 Yes | 6 No |
Answer / nitin arora
It depends on the voltage rating of the transformer
IF transformer rating is less than 72 KV then minimum BDV should be 30 KV.
IF transformer rating is 72 to 170 KV then minimum BDV should be 40 KV.
IF transformer rating is more than 170 KV then minimum BDV should be 50 KV.
All above results are referring the 2.5 MM gap during test.
Is This Answer Correct ? | 6 Yes | 0 No |
For veryfication of oil purity every year to be checked the
BDV(breakdown voltage),we have take out the transformer
oil in the transformer and collect in the high voltage kit
inthe kit two stem will be there within the 2mm gap and
then apply the high voltage 50kv for 1 minute and it
shiould be withstand upto the mentioned time.Otherwise oil
to be filtered.
Is This Answer Correct ? | 24 Yes | 38 No |
with out colour codeing on conductor how can be find what is r,what is b,what is y phases.....
WHAT KIND OF LIGHTENING PROTECTION SCHEMS CAN BE ADOPTED FOR THE FLAT ROOF OF BIG DIMENSION.
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
What is LT Breaker Panel?
If increased the frequency up to 1000 then what changes shows in voltage?
Formula to calculate amps rating when we are having only the width & thickness of the coppper ?
How conventional fire alarm system works?
we have 15 ampere variyac but we want 30 ampere variyac what we do
what are the major difference between 3phase 3wire and 3phase 4wire trivector meter?
rrb question
How Id and Ires are calculated in siprotech 7ut612 and abb trsfmr differential relay.what is the formula
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?