what is the breakdown voltage value in BDV test in
transformers?
Answers were Sorted based on User's Feedback
Answer / sudhansu kumar dalei
The BDV of oil in transformer is 60 KV/1 min within the gap
of 2.5mm in the test vessel of oil test kit.
| Is This Answer Correct ? | 77 Yes | 10 No |
Answer / rajesh kumar.k
As per IE rule it should withstand 40kv/min.
| Is This Answer Correct ? | 39 Yes | 12 No |
Answer / yog111283
as per rule. after oil filteration oil sparking value must
be more than or at list 60 kv
| Is This Answer Correct ? | 30 Yes | 12 No |
Answer / kishore
the minimum aceptable value of breakdown voltage in BDV
test is >30KV
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / nitin arora
It depends on the voltage rating of the transformer
IF transformer rating is less than 72 KV then minimum BDV should be 30 KV.
IF transformer rating is 72 to 170 KV then minimum BDV should be 40 KV.
IF transformer rating is more than 170 KV then minimum BDV should be 50 KV.
All above results are referring the 2.5 MM gap during test.
| Is This Answer Correct ? | 6 Yes | 0 No |
For veryfication of oil purity every year to be checked the
BDV(breakdown voltage),we have take out the transformer
oil in the transformer and collect in the high voltage kit
inthe kit two stem will be there within the 2mm gap and
then apply the high voltage 50kv for 1 minute and it
shiould be withstand upto the mentioned time.Otherwise oil
to be filtered.
| Is This Answer Correct ? | 24 Yes | 38 No |
How to test REF relay testing for LV panel as per Kahramaa standard?
if the diameter of a conductor is 'R' then what is the distance between two bundle conductor in a phase?
HOW TO CALCULATE LV CABLE SIZING?
What do you mean by creepage distance?
What is the difference between electrical earthing and electrical grounding?
Shall we use Dyn1 transformer in place of Dyn11 for motor application as a distribution transformer
IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?
is it possible for different brand of H.V transformers to run or operate in parallel to each other? if so how much disturbance can this affact the H.V bus bar?
During Millivolt drop test current leads are applied in the extreme ends and voltage leads are given just before the current leads.. what will be the difference if voltage leads are given in the extreme ends? and why?
what happens to the speed of a DC series motor when series field winding is removed?
What are all the points to be checked for a newly re-winded motor before installation
How to protect a Dosing pumps/any sensitive equipment (single phase) from surge protection inside a food factory.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)