Answers were Sorted based on User's Feedback
power factor is simply the angle(phase) diffrence b/w the
voltage and current wave in a system.
in case of d.c. voltage, as it is not a fluctuating wave,
the resulting current is also non fluctuating. thus no
phase angle exists b/w them.
| Is This Answer Correct ? | 22 Yes | 0 No |
power factor is the cosine of angle between voltage and
current. In case of DC the angle between voltage and
current is zero. therefore power factor always remains 1.
power factor= cos(angle between vtg and current)
here angle = zero
therefore power factor = 1
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / s.rajasekar
dc is the directcurrent it has no phase difference between
the voltage and current is unity or zero.so we won't
consider about PF
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / abhi...
In dc there is no phase difference between current& voltage
(is zero) so.........
power factor= cos(angle between vtg and current)
here angle = zero
therefore power factor = 1
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / syed vikhar ahmad
as we know power factor is the cosine of the angle between
voltage and current and in dc there is 0 angle between
voltage and current so the power factor is always one thats
why we dont discuss power factor in dc.
| Is This Answer Correct ? | 1 Yes | 0 No |
how braking & making capacity of circuit breaker is calculated?
What are the advantages of autotransformer?
how capacitor pass ac voltage practically?with increase frequency and cpacitance?
what is meant by carrier aided trip protection in transmission line
how to calculate the cable size
How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.
why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)
What is 100% protection of generator? Why 100% is not used but 95% is generally used?
What is the basic difference between directional and non directional over current protection?
Two electrically operated Vibro Motors are fixed in parallel direction in vibrating feeder. What is the direction of both Vibro Motors?
I have a 33 KV sub stn with two mother transformers 33/11 KV of capacity 3150 and 1600 KVA respectively. The total connected load 16809 KVA(11/0.433KV).how i calculate the max current & how i decided the CMD.
Will a load of 15A work if we connect it between one phase and earth?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)