Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why three wire is using with a RTD?

Answers were Sorted based on User's Feedback



Why three wire is using with a RTD?..

Answer / guest

Resistanc Temperature Detector(RTD)encorporates two basic
concepts

1)Variation of temperature varies the resistance of Pt wire.
2)Variation in resistance affects the balancing of DC
bridge circuit.

For measurement purposes lead wires are brought out to make
external connections.These lead wires have some resistances
which affects the bridge balancing.

Since we can not reduces the resistances of lead wire to
zero.So, either 3 wire or 4 wire connection is employed to
ELIMINATES THE IMBALANCING TO THE BRIDGE CIRCUIT caused by
resistances of lead wires so that an accurate measurement
can be made.These wires(3 or 4) are called compensating
leads.

Author:arbelectbit@yahoo.com

Is This Answer Correct ?    29 Yes 4 No

Why three wire is using with a RTD?..

Answer / sam

You are right, and the temperature indication does not
increase so significantly that it is worth the effort to use
a 3 or 4 wire RTD.
It might increase with something like 0,001Deg C so that is
so small you might as well say there is no difference in the
accuracy of a 2,3 and 4 wire RTD, using a local or smart
transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck

Is This Answer Correct ?    14 Yes 0 No

Why three wire is using with a RTD?..

Answer / maswood alam

Actuly there is little diffrence b/w 3 wire nd 4wire, 3wire
has 95% accurcy nd 4 wire has 100% but 4 wire more costly nd
both are use as long distance so we genarally prefared 3
wired RTD System......

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

Consider a level troll. i am getting a correct value in 4mA and 20mA. the value in the middle(30 to 60%)is disturbed and i am not getting the appropriate value. what is the solution to normalize the level and to get the correct value..

2 Answers   KNPC,


WHAT DO WE MEANT BY INSTRUMENT MAINTENANCE IN SOFTWARE SIDE.

1 Answers  


What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?

0 Answers   Process Control Technologies,


what is the difference between cold loop and hot loop

2 Answers  


how to connect 3 wire 4-20 mA transmitter in Plc system PLC system and how explain how the measuring data communicate with plc system.

1 Answers  


what is the principle of vibration

3 Answers  


I have got a call of IOCL interview for projects having 2yrs experience. What sort of questions should I expect in the interview?

0 Answers   IOCL,


Close loop and open loop diagram for instrumentation

1 Answers   Petron ltd,


We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???

2 Answers   National Petrochemical Company,


what is the difference between 3,4 wire RTD sensor?

6 Answers   HTA Instrumentation,


what is the difference b/w normal thermocouple and skin type thermocouple?

1 Answers   Heisco,


There are many type of control cable like pair,core,tried, What are defination each one

0 Answers   Birla,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)