Answer / mohammed abbas
4 - 20 ma is used because one resion is that control system
like DCS AND PLC will accept (1 - 5vdc)only for that resion
by connection 250 ohm resistand accross with ( 4 - 20 ma)
we can get ( 1 to 5 vdc) (1vdc=4ma and 5vdc=20ma) this is
as per ohms law ,V=IR
IF V=4ma*250ohm=1vdc
20ma*250ohm=5vdc
(4 - 20)ma is linear with(0 -100%) and the output will get
linear from 4ma,
| Is This Answer Correct ? | 37 Yes | 2 No |
Answer / sivasankar
The base range of the electronic transmitter out put is 0
to 16 mA. but during measuring through a series DC volt
connection (24VDC)the negative reading could not be
justified either the result is wrong polarity or the actual
negative reading below Zero value. So international
accridation has decided to elevate the zero value from 0 mA
to 4mA and straight way increased span value also from 16mA
to 20mA.(as an equal increment in 5 step 0%,25%,50%,75% and
100% of out put). Generally the electronic sensor base
output reading trimmed with 2.99 to 3.22 mA from
manufacturer. if the sensor is in good condition it will
show the base reading. 5 to 20 mA reading is not accepted
in industry so far.
| Is This Answer Correct ? | 20 Yes | 14 No |
Answer / selvam
4 - 20 ma is used because one resion is that control system
like DCS AND PLC will accept (1 - 5vdc)only for that resion
by connection 250 ohm resistand accross with ( 4 - 20 ma)
we can get ( 1 to 5 vdc) (1vdc=4ma and 5vdc=20ma) this is
as per ohms law ,V=IR
IF V=4ma*250ohm=1vdc
20ma*250ohm=5vdc
(4 - 20)ma is linear with(0 -100%) and the output will get
linear from 4ma,
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sutharani.a
The electronic instrument using only dc power supply. so
using the standed value of 4-20mA, because 0-16mA is the
standared deviation elctronic meters. 0 value is not
pricise value so zero insted of four and 16 insted of 20.so
we are use to 4-20mA normal.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / naveed ahmad
due to linearity, we can't use 5-20ma because in case of 5-
20mA our 25%,50% and 75% 'll not linear.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is loop or pigtail in an impulse line?
8 Answers Qatar Airlines, Qatar Petroleums,
HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar
How the sizing of the analog signal cable is calculate?
What output voltage the proximity switch shows when it is in open enviornment?
What is the function of SMPS
How to do calibration of magnetic flowmeter
What are the types of control valves available
What is the expansion of RADAR? How it works?
how to calculate signal cable sizing? and multipair cable sizing??explain in brief?
How to calibrate the pressure Transmitters
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)