Answer / mohammed abbas
4 - 20 ma is used because one resion is that control system
like DCS AND PLC will accept (1 - 5vdc)only for that resion
by connection 250 ohm resistand accross with ( 4 - 20 ma)
we can get ( 1 to 5 vdc) (1vdc=4ma and 5vdc=20ma) this is
as per ohms law ,V=IR
IF V=4ma*250ohm=1vdc
20ma*250ohm=5vdc
(4 - 20)ma is linear with(0 -100%) and the output will get
linear from 4ma,
| Is This Answer Correct ? | 37 Yes | 2 No |
Answer / sivasankar
The base range of the electronic transmitter out put is 0
to 16 mA. but during measuring through a series DC volt
connection (24VDC)the negative reading could not be
justified either the result is wrong polarity or the actual
negative reading below Zero value. So international
accridation has decided to elevate the zero value from 0 mA
to 4mA and straight way increased span value also from 16mA
to 20mA.(as an equal increment in 5 step 0%,25%,50%,75% and
100% of out put). Generally the electronic sensor base
output reading trimmed with 2.99 to 3.22 mA from
manufacturer. if the sensor is in good condition it will
show the base reading. 5 to 20 mA reading is not accepted
in industry so far.
| Is This Answer Correct ? | 20 Yes | 14 No |
Answer / selvam
4 - 20 ma is used because one resion is that control system
like DCS AND PLC will accept (1 - 5vdc)only for that resion
by connection 250 ohm resistand accross with ( 4 - 20 ma)
we can get ( 1 to 5 vdc) (1vdc=4ma and 5vdc=20ma) this is
as per ohms law ,V=IR
IF V=4ma*250ohm=1vdc
20ma*250ohm=5vdc
(4 - 20)ma is linear with(0 -100%) and the output will get
linear from 4ma,
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sutharani.a
The electronic instrument using only dc power supply. so
using the standed value of 4-20mA, because 0-16mA is the
standared deviation elctronic meters. 0 value is not
pricise value so zero insted of four and 16 insted of 20.so
we are use to 4-20mA normal.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / naveed ahmad
due to linearity, we can't use 5-20ma because in case of 5-
20mA our 25%,50% and 75% 'll not linear.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the difference between floating and fixed voltage?
what are the definitions of input, output, command & signal according to instruments controlled by PLC using DCS System?
how to wire from pressure transmitter to marshalling panel and panel to controller and controller to dcs plz give the answer with example .
What is ultrasonic flowmeter?
what will be the output of a temperature transmitter if temperature is 120 degree celcius?
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
difference b\w a transducer and a sensor
What is linearity of RTD over 0 to 200 degC?
how u calibrate sox nox co2 co in cemps?what is opacity n HPm?tell the standard parameters of cems?
which one is best profibus or RS485 for communication?
I want to know if flowrate increases in 16' pipe line what will happen to upstream pressure and why?
What is mean by SMART in an Instrumentation. is any full form for SMART?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)