What is the difference between MPCB and OLR?
Answers were Sorted based on User's Feedback
Answer / vinod.c
MPCB is the Motor protected circuit Breaker.
OLR is the over load Relay
| Is This Answer Correct ? | 79 Yes | 30 No |
Answer / satish m
As mentioned in above answers the abbrivation is correct.
The main difference is MPCB is the combination of contactor
and OLR, it having in built OLR.
OLR- it is an element it is connected to the output of the
contactor to protect the motor.
| Is This Answer Correct ? | 48 Yes | 5 No |
Answer / sachin
MPCB is device which has inbuilt OLR+Short circuit
connected to Trip coil.
In event of fault like oveload OLR coil will sense and give
command to trip coil to trip.
In event of Short circuit fault SC coil will energise
inside MPCB and trip circuit breaker.
In case of OLR over load relay, its only a primary device
which senses only over loads.We need to connect contactor
to break the circuit.
| Is This Answer Correct ? | 44 Yes | 3 No |
Answer / nithyanandam
Mr. Vinoth everyone know that MPCB is Motor protection
circuit breaker and OLR is Over load relay.
What is the difference between them.
OLR break the circuit and MPCB also break the circuit.
Please tell me difference between these two things
| Is This Answer Correct ? | 28 Yes | 5 No |
Answer / murugesh
OLR is the relay which senses the overload current i.e more than 100% of the motor capcity, whereas MPCB breaks the circuit during shortcircuit i.e current in the range of 5 to 10 times the rated current.
| Is This Answer Correct ? | 18 Yes | 3 No |
hi. the olr and mpcb both are the protecting devices. but
the olr senses the current of winding capacity. means the
maximum current which does not cause the winding
insulation.it always connected in the starter.
but the mpcb sense the over current by means of load. the
phase to phase short, and the dead short are sensed by the mpcb.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / nithyanandam
Mr. Satish thank you for your answer.
In an Interview I'm also told the same answer. But the
Interviewer asked, "You are saying The difference with
cosidering the circuit connection only. Please tell me
difference with considering Over load current and short
circuit current. This is the major difference between them".
I'm really don't Know answer untill now. Please tell me the
answer immediately.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ravikumar
OLR - OVERLOAD RELAY
MPCB- MOTOR PROTECTION CIRCUIT BREAKER
IF SHORT CIRCUIT IS OCCURED IN CIRCUITS ,
OLR - MELT THE COIL TO TRIP AFTER ITS AUTOMATICALLY
CAME NORMAL POSITION BUT,
MPCB- TRIP THE COIL IT WILL BE MANUALLY SWITCH ON THE RUN
THIS IS THE DIFFERENCE
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / mohammed abdul naeem
1. MPCB is Trip by (Auxiliary Block Contact.)
2. OLR is Trip by Thermal (heating by range setting)
| Is This Answer Correct ? | 4 Yes | 1 No |
what is transformer
the problem faced on star or delta winding connection??
To test Transformer we give HT side 440V to see wheather that it is producing 17.6V on LT to verify Voltage ratio is correct or not but when we give the 440V voltage to LT side then what will happen to HT voltage ?
difference between brush less & brush excitation in a generator?
how is working d.c amps meter?how to connect the dc ammeter inthe circuite?
What is the difference between vector surge relay (78) and Pole slip relay (98G)
how can we chack a capacitor in acircuit
What is polarisation index value?.(pi value) Simple & brief definition of polarisation index?..
what is diffrence between dc motor and dc generator?
What is difference between metal clad & metal enclosed switchgear?
11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The rated current is 26Amps. Application is for the blower. The motor takes ( no load without coupling impller ) only 2.5A and 5Amps in star & delta starter test.Need to know why its taking high current.
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)