why firewall is build up between two transformer
(220/11kv,50MVA)?what should be the firewall height?what is
the clearance between firewall and transformer?
Answers were Sorted based on User's Feedback
Answer / rakesh singh
Fire wall is built up between two transformer to protect
one transformer in case of firing on the other
transformer,the hight should be 1.5 times of the height of
the longer transformer and minimum clearance between fire
wall and transformer should be one meters.
| Is This Answer Correct ? | 27 Yes | 5 No |
Answer / engineered
as per indian electricity rule height fire wall shall be
more than height of heighest transformer.
| Is This Answer Correct ? | 5 Yes | 0 No |
One 200 V, 100 W bulb is connected in series with primary of a 200 V, 10 kVA transformer. If its secondary is kept open circuited, then the bulb would have (1) Full brightness (2) Poor brightness (3) A little less than full brightness (4) More than full brightness...explain
what is saturation kit?which use above 15 kw motors panel side.
When lag/lead/lag-lead compensation is employed?
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
Why battery is always operate on dc supply?
1 Answers Vikram Ispat Industries,
if we run a 3 phase machine on two phase what will happend??? given answer with solid reason please
what effect will 10 milliampere current cause to human body
Why use in ht motore
how to find ratio of CT & PT in 66/11kv 12 mva supply system ? explain with calculation.
what is the principle of servo motor
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
how to calculate the neautral earthing conductor size for a 500kva dg set.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)