why firewall is build up between two transformer
(220/11kv,50MVA)?what should be the firewall height?what is
the clearance between firewall and transformer?
Answers were Sorted based on User's Feedback
Answer / rakesh singh
Fire wall is built up between two transformer to protect
one transformer in case of firing on the other
transformer,the hight should be 1.5 times of the height of
the longer transformer and minimum clearance between fire
wall and transformer should be one meters.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / engineered
as per indian electricity rule height fire wall shall be
more than height of heighest transformer.
Is This Answer Correct ? | 5 Yes | 0 No |
why use celling fan wing is two or three ?
Explain cos(theta) and Sin(theta)
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
can i connect wavetrap in 2 different phase in EHV line?
how many test is necessary for 27mva transformer.
What we change frequency from transformer. yes or no
if grounding is notdone at regular intervals for long distance transmission, will the load connected at distribution end receive voltage during negativehalf cycle of the sine wave?
What is the role of a Production Engg in a Industry?????
full form of electrical?
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
What is the difference between online ups and offline ups?
44 Answers Electrical Tech, GMR, Gravity India, HCL, Indus Towers, NIT, Pyramid, Techno Electric and Engineering, UBS,
what is use of reactive power in ac ckt.