why firewall is build up between two transformer
(220/11kv,50MVA)?what should be the firewall height?what is
the clearance between firewall and transformer?
Answers were Sorted based on User's Feedback
Answer / rakesh singh
Fire wall is built up between two transformer to protect
one transformer in case of firing on the other
transformer,the hight should be 1.5 times of the height of
the longer transformer and minimum clearance between fire
wall and transformer should be one meters.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / engineered
as per indian electricity rule height fire wall shall be
more than height of heighest transformer.
Is This Answer Correct ? | 5 Yes | 0 No |
what will happen if one of the phases from a 3-phase motor is disconnected?? stop/run at 2/3rd speed or run at same speed????
How many kinds of E.L.C.B and how to work E.L.C.B
What is the suitable rating of MCB used for 1.5 Ton A.C & why?
why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?
What is the d/f between DOL & star delta starter & automatic star delta starter?
23 Answers ACC, Dalkia, Engineering, Indeco, NINL, Novotel, RMH Control Systems, Wipro,
over frequency is the protection of turbine or alternator?
in dc suppy frequency is zero why? if dc frequency is zero how to exist dc transients and ac transients
what mean by machin
why is fan rotating slow speed, what is the problem?
How to calculate PF capactors for a connected load?
Main advantage of auto transformer over two windings transformer is that A it needs no cooling B it uses only one winding C core losses are reduced D it has simple construction
Starting Time of LT & HT Motor