Answer / iamdon
Taps are provided on high voltage(HV) side in tap changing
transformers.
The reason behind this is that in a transformer, low
voltage windings are placed close to core so that
insulation requirement is less.The high voltage windings
are provided on outer layers.It is physcially easier to
putting taps and handling it from the windings which is
clearaly accessible.There are more number of turns on HV side
which makes it easier to obtain fine variation in voltages.
So the choice of HV windings for taps is justified.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / dilawar husain
The reasons given in above answers are correct. But there
is one more important reason and that is current. On Lv
side the current being more it needs heaviour contacts as
compared to HV side where the current is far less and
easier to handle. Also in case of ON LOAD Tap changers the
current is divirted to a bypass circuit for the duration
the tap is changing the pposition. This bypass circuit is
easier to design for lesser current on High voltage side.
| Is This Answer Correct ? | 4 Yes | 0 No |
How cable from Kit-Kat to main switch, from starter to motor are designed?
explain why tap changer is always connected to high voltage winding side of the transformer.
why name plate detail HP/KW rating of a motor is different from measured value HP/KW using formula?
what is purpose of using neutral grounding transformer in generators??
up to what extwnt of voltage the celing fan works?
Difference Between Differential Relay and Restricted Earth Fault Relay of Power Transformers
What is the resistance of the field winding of a d.c. Shunt generator kept low?
What is Control & Relay Panel? And Remote Control Center?
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
how to control the generator output voltage? what r the condition should satisfy for synchronization?
How i can select current transformer and meters for the upgrading the panal..for 200kw to 600kw....i need to select monitoring and protection ct,s and apmpire meter ,kw meter too.
what is Basic Engineering.,FEED and Detail Engineering with respect to Electrical Engineering.(Explain with Example)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)