Answer / rajkumar r
By varying FIELD excitation we can control the output of DG.
Practically by changing AVR setting we can control the
output of DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. Speed/frequency should be the same
4. Load impedance should be the same.
| Is This Answer Correct ? | 27 Yes | 3 No |
Answer / rvg.msceb
to be very clear, in commercial generator, nobody using
separated excitation system. self excitation is the best
method unless some specific reasons.
For controlling output voltage, a device called AVR,
automatic voltage regulator to be used, and it sense the
output voltage at each instance, and adjusts accordingly.
these are the condition for syncronization.
1.phase sequence of both generators should be same.
2-frequency shuld be same.
3-terminal voltage shuld be same.
4.both generators should have nearly same percentage
impedence.
| Is This Answer Correct ? | 24 Yes | 1 No |
generator out put voltage is controlled by varying
excitatoin.
for syncronising of generator :
1 phase sequence should be same
2. voltage and frequency should be same and one most
important
3. phase angle should be same
| Is This Answer Correct ? | 17 Yes | 4 No |
Answer / prembujju, park institutions
To control the output of the generator we have to consider the
following conditions
1. phase sequence will be same
2.terminal voltage will be same
3.frequency will be same,
if we change the speed of the prime mover we can get
controlled generator output. but fuel input increases which
changes the frequency also. so system not matches for those
three conditions.
on other hand the output of the generator can be
controlled by increasing or decreasing the excitation
depending of the load demands.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / pravesh
By varying FIELD excitation we can control the output of DG.
Practically but commertial d.g. sets are controlled by self
excitation and avr controls the output voltage output of
DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. frequency should be the same
4. percentage impedance should be the same.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / pavan
By varying the turbine speed. voltage, frequency & speed are
to be consider for synchronization.
| Is This Answer Correct ? | 5 Yes | 19 No |
Answer / pradeep kumar rawat
by contoling the fuel we can contol the output voltage of
generator.
condition for syncronization.
1-phase sequence shuld be same.
2-frequency shuld be same.
3- terminal voltage shuld be same
| Is This Answer Correct ? | 3 Yes | 24 No |
why we are using in reverse power relay in generator singranizing
What is the ideal power factor?
what topics we have to concentrate for power grid et.written test.and tell what to read for english synonyms and antonyms.
What is an Air COmpressor
Differenc between the resistance and resisters?
what is relation between vector group of transformer and its load hormonics?
25 kvar capacitor , how much current ? For 25 KVAR--Capacitor I = ?
What is a charge.?
What does OHB stand for in specifications for circuit breakers, especially found in SF6 circuit breaker?
what is VFD and where is use of it
1. What is the exact formula for one weber? for example,(one ampere = one coulomb electron of electrons crossing a point of conductor at one second. i.e, 1A=1Q/1sec)
what is droop?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)