how to control the generator output voltage?
what r the condition should satisfy for synchronization?
Answers were Sorted based on User's Feedback
Answer / rajkumar r
By varying FIELD excitation we can control the output of DG.
Practically by changing AVR setting we can control the
output of DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. Speed/frequency should be the same
4. Load impedance should be the same.
| Is This Answer Correct ? | 27 Yes | 3 No |
Answer / rvg.msceb
to be very clear, in commercial generator, nobody using
separated excitation system. self excitation is the best
method unless some specific reasons.
For controlling output voltage, a device called AVR,
automatic voltage regulator to be used, and it sense the
output voltage at each instance, and adjusts accordingly.
these are the condition for syncronization.
1.phase sequence of both generators should be same.
2-frequency shuld be same.
3-terminal voltage shuld be same.
4.both generators should have nearly same percentage
impedence.
| Is This Answer Correct ? | 24 Yes | 1 No |
generator out put voltage is controlled by varying
excitatoin.
for syncronising of generator :
1 phase sequence should be same
2. voltage and frequency should be same and one most
important
3. phase angle should be same
| Is This Answer Correct ? | 17 Yes | 4 No |
Answer / prembujju, park institutions
To control the output of the generator we have to consider the
following conditions
1. phase sequence will be same
2.terminal voltage will be same
3.frequency will be same,
if we change the speed of the prime mover we can get
controlled generator output. but fuel input increases which
changes the frequency also. so system not matches for those
three conditions.
on other hand the output of the generator can be
controlled by increasing or decreasing the excitation
depending of the load demands.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / pravesh
By varying FIELD excitation we can control the output of DG.
Practically but commertial d.g. sets are controlled by self
excitation and avr controls the output voltage output of
DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. frequency should be the same
4. percentage impedance should be the same.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / pavan
By varying the turbine speed. voltage, frequency & speed are
to be consider for synchronization.
| Is This Answer Correct ? | 5 Yes | 19 No |
Answer / pradeep kumar rawat
by contoling the fuel we can contol the output voltage of
generator.
condition for syncronization.
1-phase sequence shuld be same.
2-frequency shuld be same.
3- terminal voltage shuld be same
| Is This Answer Correct ? | 3 Yes | 24 No |
why we use Test Terminal Block in 11 KV and 33 KV electrical panels.
29 Which of the following breaking method save energy? A regenerative breaking B plugging C dynamic breaking D none of above
HOW COULD A SINGLE PHASE INDUCTION MOTOR ROTATE IN OPPOSITE DIRECTION???
Write masons gain formula.
why the no.of slots in stator in not equal to the no. of stator in rotor in induction motor????
can any one explain me the where is the use of plc and scada
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
i have gear oil pump with single phase motor.some time its motor starts running in reverse direction rather than forward direction...whats the reason behind this issue. 1- either capacitor is week? 2- or winding is week?
if we have a power factor 0.99 and we add a capacitive bank with it then what happen?
star delta starter single line digram
Difference between On Line capacitor and Station Type capacitor.
Which element has power dissipated in it when the source is removed ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)