how to control the generator output voltage?
what r the condition should satisfy for synchronization?
Answers were Sorted based on User's Feedback
Answer / rajkumar r
By varying FIELD excitation we can control the output of DG.
Practically by changing AVR setting we can control the
output of DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. Speed/frequency should be the same
4. Load impedance should be the same.
| Is This Answer Correct ? | 27 Yes | 3 No |
Answer / rvg.msceb
to be very clear, in commercial generator, nobody using
separated excitation system. self excitation is the best
method unless some specific reasons.
For controlling output voltage, a device called AVR,
automatic voltage regulator to be used, and it sense the
output voltage at each instance, and adjusts accordingly.
these are the condition for syncronization.
1.phase sequence of both generators should be same.
2-frequency shuld be same.
3-terminal voltage shuld be same.
4.both generators should have nearly same percentage
impedence.
| Is This Answer Correct ? | 24 Yes | 1 No |
generator out put voltage is controlled by varying
excitatoin.
for syncronising of generator :
1 phase sequence should be same
2. voltage and frequency should be same and one most
important
3. phase angle should be same
| Is This Answer Correct ? | 17 Yes | 4 No |
Answer / prembujju, park institutions
To control the output of the generator we have to consider the
following conditions
1. phase sequence will be same
2.terminal voltage will be same
3.frequency will be same,
if we change the speed of the prime mover we can get
controlled generator output. but fuel input increases which
changes the frequency also. so system not matches for those
three conditions.
on other hand the output of the generator can be
controlled by increasing or decreasing the excitation
depending of the load demands.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / pravesh
By varying FIELD excitation we can control the output of DG.
Practically but commertial d.g. sets are controlled by self
excitation and avr controls the output voltage output of
DG.
Conditions for synchronization:
1. Phase sequence should be the same
2. Terminal voltage should be the same
3. frequency should be the same
4. percentage impedance should be the same.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / pavan
By varying the turbine speed. voltage, frequency & speed are
to be consider for synchronization.
| Is This Answer Correct ? | 5 Yes | 19 No |
Answer / pradeep kumar rawat
by contoling the fuel we can contol the output voltage of
generator.
condition for syncronization.
1-phase sequence shuld be same.
2-frequency shuld be same.
3- terminal voltage shuld be same
| Is This Answer Correct ? | 3 Yes | 24 No |
why transmission line 11Kv OR 33KV,66Kv not in 10kv 20kv?
43 Answers A2Z Group, Baiji Power Plant Gas, Electrical, HCL, Kirloskar, Mepco, NEPC, OAMC, UNI, University of Lahore,
Why we are mention U1, V1, and W1 in primary side of transformer give technical reason
generally in LT and MV motors we are using 3.5Coresx16,25,35,50 etc cable for supply.although motors is earthed at two point and having all protection.then why we are using that 1/2 core for earthing the motors.while in HT cable we are using only 3core cable for motor supply.generally lt and mv motors are delta connected and ht motors having star connection.whethere it is having any relation with winding connection( star or delta).all motors i am talking about are dol only.can anybody solve my confusion.thanks...
What type of fittings and electrical accessories can be install in radiation area ?
sir , what happen if we decrease ( approx 3 inch ) the lenth of shaft in 110KW Induction , three phase motor. actually a 110KW motor is couppled with star couplling to 120TR compressor. When we doing maintenance in compressor it is required to skid the motor backword and resulting dis- alightnment . so we want to change the tyre coupling in place of existing coupling. so it is required to cut off the rotor aprox 3 inch form driving side.
what r substations?what r there work?why voltages r incresed and then reduced during distribution of power
Before given the connection to Alternator (pre- commissioning) which tests we will conduct
one conductor length is L.and i am strech uniformly this conductor and made length is 2L.so resistance of this strech conductor is R=4R..but i want to know about area of stech conductor hows it become a/2..
On what principle reluctance motors work?
how to convert 1 phase power to 3phase power by using induction motor. . . .
Does voltage and current can be seperated?
What is the name of process In VFD frequency are increase then voltage increase & frequency decrease then voltage decrease?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)