Difference Between Differential Relay and Restricted Earth
Fault Relay of Power Transformers
Answer / k.prakashchandra
Differential relay compares the correspondig currents of
the same phase on both sides,where REFR compares the
unbalanced current of the phases with the current in the
neutral
Is This Answer Correct ? | 11 Yes | 0 No |