explain why tap changer is always connected to high voltage
winding side of the transformer.
Answers were Sorted based on User's Feedback
Answer / inderpreet singh
There are many Advantages/reasons that the tap changer is connected to High voltage, some are described below:
1.HV winding is easy to Tap because HV winding is always placed on LV winding and LV winding is placed near to core due to insulation and cost constraints.
2. For keeping voltage at consumer end constant, Tap changer is provided on HV side.
3 In Electromagnetic field theory, Voltage & Current are inversely proportional to each other. where voltages are high currents will be low, when tap changer is connected to HV it will lead to avoid heavy inrush of current while tap changed.
Is This Answer Correct ? | 110 Yes | 5 No |
Answer / d4
The HV windings are placed on the LV windings, so it is easy
to take tappings from the HV side. Also the currrent in the
HV side is less than that on the LV side; this helps in
reducing the arcing which takes place as a result of tap
changing.
Is This Answer Correct ? | 35 Yes | 4 No |
Answer / zahid khan
tape changer is always connected to high voltage winding
side of the transformer to avoid heavy inrush current
Is This Answer Correct ? | 41 Yes | 16 No |
Answer / mithun
Actually a tap changer is used to get variable voltages. It
is just an air break switch. If it is connected in high
current side (LV side), there is more chances to occur
heavy sparks while in changing the taps, means while
changing the switch positions. In order to avoid that heavy
sparks in high current side, tapings are provided on low
current (HV side).
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / k.rajmohan
The reason is current in HV is less than LV. The word
alway in question is not correct. The reason due
insulation problem some time tapchanger is plased in LV
side of the transformer.
Is This Answer Correct ? | 14 Yes | 8 No |
Answer / asad
It is difficult to tap the l.v winding since it is placed near to the core due to insulation consideration. it is easy to tap the h.v winding because it is outside the l.v winding, easily accessible and therefore can be tapped easily
Tap changers on the h.v side carry low current though more insulation have to be provided.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vyankatesh badgujar
simply to avoid matter of rich current concern and it's always easy to provide tapping on outermost than innerone, as hv is outer winding.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maurya kishan
High tension side me current ki Kumar kam hoti hai jisase tap changing gear ki size kam rakhani padati hai so.............
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / brajesh kumar chaudhary
Tapping ka main work voltage ko jarurat ke anusar voltage ko badhane ya ghatane ke liye hota hai. aur isko secondry side me lagate hai
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / nidhi
to avoid high losses in case of not full load supply. when
smaller amount is required then it can be connected to that
Is This Answer Correct ? | 6 Yes | 20 No |
what is level 2 automation?
when transformer oil should be filtered/tested?
what is function of reactor coil in Power factor correction panel
Why the transformers are rated in kva?
11 Answers Birla, NTPC, Reddy Labs, Vijai Electricals,
what must be the mf for a meter with the following conditions. line ct ratio-100/1 line pt ratio- 220kv/110v meter pt ratio- 3X63.5V meter CT ratio- -/1 A
Lt trivector meter with ring type CT.Spec of meter are 3x240 v, -/5A. Ring ct spec. are 60/5A, line voltage- IL .66/3.0KV..what is the multiplying factor
why we generate transmit and distribute electrical supply in multiple of 11
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
if i have 5kw,9A,three phase induction motor,if i want to install it 100 meter away from its feeder,how i will culculate cable size for this load.
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
What is the meaning of TRI Vector meter?
7 Answers ABB, Excel Power Switchgear,
Sir, I completed DEEE... And now I working in TNEB for one year apprenticeship. If I eligible for applying c license and how can I get?