calibration of instruments.
Answers were Sorted based on User's Feedback
Answer / gomathi sankar
Calibration of instruments is nothing but comparing the
actual value of the instrument which u use with the
standard value of that instrument model.
Is This Answer Correct ? | 29 Yes | 2 No |
Answer / raffi
Calibration procedure:
calibration equipment: calibrator with handpump
For ex: Range of Transmitter is 0-100psi
Step1: connect the calibrator to the transmitter
Step2: connect the multimeter in series with transmitter to
verify the transmitter o/p in mA
step2: Apply the pressure to the transmitter by hand pump
in calibrator
Step3: compare whether both calibrator and the transmitter
showing the same value.if you applied 50 psi throuhg the
calibrator then the transmitter should have to show the
same value.If you find any error.Do the zero/span
Adjustment.by adjusting the zero/span screw
increasing/decreasing
step4: compare the transmitter and calibrator as per follows
calibrator Transmitter Transmitter o/p
in psi in psi in mA
0 0 4
25 25 8
50 50 12
75 75 16
100 100 20
Is This Answer Correct ? | 22 Yes | 0 No |
Answer / vasu
Calibration of instruments is nothing but comparing the
actual value of the instrument which u use with the
standard value of that instrument model......
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / bill
If an instrument operates throughout it's full range
with linearity and porportionality when compared to
an NIST Standard, it is considered in calibration
( National Institute of Standards and Technology )
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / joseph
cALIBRATION IS NOTHING BUT THE COMPARISON BETWEEN THE
STANDERED VALUE AND THE MEASURED VALUE.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / sakthisithardhan
Calibration is the process of to set an instrument to show
the reading in between allowable scale....
example 0-10V meter
if ponter shows <0 means v've to calibrate it to show exact
0.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / rajiv mehta
To check whether the instrument in use is with in the
standard parameters
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / narenkumar1985
calibration equipment: calibrator with hand-pump
1: connect the calibrator to the transmitter
2: connect the multimeter in series with transmitter to
verify the transmitter o/p in mA
3: Apply the pressure to the transmitter by hand pump
in calibrator
4: compare whether both calibrator and the transmitter
showing the same value.if you applied X psi through the
calibrator then the transmitter should have to show the
same value.If you find any error.Do the zero/span
Adjustment.by adjusting the zero/span screw
increasing/decreasing
5: compare the transmitter and calibrator as per follows
with a desired range of an instrument with o/p 4-20mA
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vivek saini
CALIBRATION of INSTRUMENT IS A TESTING OF ACTUAL VALUE ie:- value which is calculated WITH THE NATIONAL INSTITUTE OF STANDARDS AND TECHNOLOGY (NSIT) VALUE GENERALLY DONE FOR CHECHING THE ACCURACY OF INSTRUMENT.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rafiq
calibration is nothing but the "testing" . it compares the
actual value to real value and realise that value takes the
decisions
Is This Answer Correct ? | 2 Yes | 3 No |
Questions on flow meters,few questions on HART protocol,
Explain the thermocouple and RTD?
what is the meaning of potential free contact. difference between dry and wet contact?
Where Can i take a SPI INtools training in Mumbai? In Rolta India Ltd to whom I should approach regarding of SPI INtools Training?
can we copy the software from a transmitter using hht(hart 275) ?
Why flow/pressure transmitter before control valve?
what are the values of fuel flow rate in various places in boiler.
why using 4-20ma not using 0-20or why not using 1- 20ma???????
WHAT ARE THE INSTRUMENTAL DIAGRAMSOF VALVES?
0 Answers Artikal, ITC Infotech,
What is fault tolerent system
Decibel.
what is the reason for flow fluctuations happen on differential flow transmitter during in service