what is hot loop check and cold loop check.
Answers were Sorted based on User's Feedback
Answer / guest
A Cold Loop check is cold because it is done without
powering the loop.
A cold check consists of checking wire continuity from the
field instrument through junction boxes and through DCS/PLC
marshalling panel terminals to the control panel. Once
continuity has been confirmed, then a Hot Loop Check is
performed on the Loop's I/O.
A Hot loop check is 'hot' because it is done with the loop
powered up.
A Hot loop check consists of
- simulating a process input at the field instrument and
then checking the instrument's output and the response to
the process signal input at DCS/PLC.
- simulating outputs at the control end and checking for
correct response at the field end.
Carl Ellis
Measure First
| Is This Answer Correct ? | 13 Yes | 1 No |
Hot loop check is power up checking .cold loop checking is continuity only.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / krishnan kumar sharma
Hot loop cheak on point stabilise the instrument in field and the cold loop cheak from the junction box to DCS /PLC .
| Is This Answer Correct ? | 0 Yes | 0 No |
what is meant by calibration
why 8bit microprocessor referred as 2^16?
What are the key features of a Distributed Control System? describing the various layers (sensor through to business system interfaces) as well as the hardware, software and security aspects of the DCS.
if we have 450 mm heigth boiler drum level ,so what is span & zero value for a dpt tranmitter
What is Cryogenic?
what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?
How to do ma trim in massflow meter?
Why 250 or 500 ohm load resistance is use in any transmitter
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
How a Flow Transmitter Works?
Types of contol loops
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)