Answer / chr
5P10 DETERMINES 5% ERROR IN MEASURING DATA FOR 10 TIMES THE
CURRENT FLOW IN THE CT.
| Is This Answer Correct ? | 37 Yes | 3 No |
Answer / r. r. patange
In 5P10, P stands for protection, there are two main
classification of current transformer
1) Metering CT
2) Protection CT
so above mention CT can be use for protection purpose.
the first digit (5) stands composite error.
composite error - it nothing but the differance between
instanteneous RMS valuve of primary current and secondory
current, multiply by transformer ratio.
the last digit (10) is stand for the times of primary
current. It means this protection CT can capable of
measuring current of 10 times than its rated during fault
condition with error of 5% and without getting saturated.
| Is This Answer Correct ? | 31 Yes | 3 No |
Answer / barkha thakur
P indicates the protection level & 5 indicates the accuracy
it means when sec current is increased by 10 times, ct
senses the current with 5 % error
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / sangram
first i explain the term:- 5 is a class of accuracy, p you
should use for protection purpose, 10 you should load up to
10VA.
you should use this CT for protection purpose, and the
burden rating should 10volt Amp at 100% load pass in
primary, you should allow +/-5% error for this CT.
| Is This Answer Correct ? | 14 Yes | 7 No |
Answer / wasim maniyar
For example, CT is specified as 15VA, 5P10 where 15VA denotes burden, 5 denotes composite error and 10 denotes ALF(Accuracy Limit Factor).
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / faheem
according to my study the there are two type of accuracy
class 5p & 10p 5p=+-1 % error,and 10p=+-3% error.and last 10
shows the accuracy limit factor 5,10,15,20 and 30.. It means
this protection CT can capable of
measuring current of 10 times more than its rated during fault
condition with error of +-1% and without getting saturated.
| Is This Answer Correct ? | 0 Yes | 7 No |
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
Why annealing is done on transformer core manufacturing process?
difference between Ac and Dc mcb ????
with out colour codeing on conductor how can be find what is r,what is b,what is y phases.....
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
What is LCI drive & how does it work & why it is used?
what is difference b/w earth and ground?
What is core CT & it's function?
what is acceptance test in electrical engineering.
Formula to calculate amps rating when we are having only the width & thickness of the coppper ?
what is short circuit force ? How to calculate it for Panel?
what is FACTS & where i can material regarding to facts.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)