what is merz price protection
Answers were Sorted based on User's Feedback
Answer / nitin lothe
Its the protection scheme used for Power Transformers to
detect internal faults n also termed as Differential
Protection. If there is difference in currents on HV and
corresponding LV side of transformer of the same phase,
protection will operate.
Is This Answer Correct ? | 118 Yes | 18 No |
Answer / shyam kishor
Merz-Price protection is the method used for protection of alternators. it is a most common system used for the protection of stator winding faults employs circulating current principle. in this scheme of protection,current at the two ends of the protected section are compared. under normal operating conditions,these currents are equal but may become unequal on the occurrence of a fault in the protection section. the difference of the currents under fault condition is arranged to pass through the operating coil of the relay. the relay then closes its contacts to isolate protected section from the system.(Ref. book on power system v.k mehta and rohit mehta)
Is This Answer Correct ? | 65 Yes | 8 No |
Answer / sudipt jena
Merz Price is also called Differential protection. And is used to protect alternator and also transmission line.For this we have two engage CT's at both the ends of the portion/equipment to be protected. In this method breaker trips, if fault occurs within both the CT's only, and not for outer zone.
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / satish
This type of protection provides a continuous check on faults within the points, where the C.T.s are used as in shown in fig 2. There are two sets of C.T.s; each set is mounted on either end of the stator phase. The secondaries of these current transformer sets are connected in star and their ends are connected together through pilot wires. The over current inverse time relay is connected across the equipotential points in the pilot wires, which will naturally be in center of these wires as shown in fig 2. But it’s convenient to locate these relays adjacent to the main circuit breaker; this can be achieved by inserting balancing resistance in series with the pilot wires to achieve equipotential point near the main circuit breaker as shown in fig 3. If there is no fault in the generator, same current will pass through the C.T.s at both the ends and there will be no current spilling into the relay.
Now if earth fault occurs as shown in fig 2, there will be an increase in current through set C.T.1 as compared to current through C.T.2. Thus there is no current balance any more resulting into spilling of current through the relay R hence tripping the circuit. If there is short circuit between the two phases as in fig3 it will also cause operation of relay R and tripping of the circuit breaker. This scheme does not provide protection for the turns of same phase
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / vinay
merz pricr protection mean voltage will be balanced under
no fult condition if fult occur it will unbalanced
Is This Answer Correct ? | 31 Yes | 30 No |
Ho de we calculate the line loss of a 500 kv line over 1000km.
how to choose the cable rating for load (KW)? EXAMPLE.50KW load
14 Answers ACC, NCUI, Polycab, PowerSol, Siemens, SW,
what is the purpose of taking HV test in LT panel.
describe your self.
ALL HT /LT PANEL TEST? DISCRIPTION.
how to make an earthing certificate
how to select cable size?
Can we use delta-star neutral grounded 3 phase power transformer bi-directionally.
You required 5A from the transformer but you get 8A. How do you minimize this?
What is DC power factor??
How many lightning arrestors to be installed on 50MX60MX10M building and is there any formular for that?
What is meant by reactance voltage?