Answer / prof. nazar m. karyar
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit
conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that
represents the direct current resistance for a one thousand
circular mils conductor that is one thousand feet long, at
an operating temperature of 75º C. The direct current
constant value to be used for copper is 12.9 ohms and 21.2
ohms is used for aluminum conductors. The “K” constant is
suitable for alternating current circuits, where the
conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating
current circuits No. 2/0 and larger must be adjusted for the
effects of self-induction (skin effect). The "Q" adjustment
factor is determined by dividing alternating current
resistance as listed in NEC Chapter 9, Table 9, by the
direct current resistance as listed in 2. Feeders – This FPN
recommends that feeder conductors be sized to prevent a
maximum voltage drop of 3%. The maximum total voltage drop
for a combination of both branch circuit and feeder should
not exceed 5%. [215-2(d) FPN No. 2],
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shoebullah
with referance to prof.nazar
answer ... Cant we calculate
voltage drop by this formula
Vd= IZ
where Z= R*cos(pi) + X*sin(pi)
and R= r*1/1000, X=
x*1/1000 ......... I am
suggesting in this way also
we can find voltage drop of a
cable ....... And further we need
to calculate percentage of
voltage drop by this formula
%Vd= sq.root of 3 * Vd/VL
*100
where VL Is line voltage ... It
should be <3% for main
distribution board <5% for all
distribution board
Is This Answer Correct ? | 0 Yes | 1 No |
Why a transformer Noise during its running condition ?
How Calculet The UPS AH In Load
differentiate between c curve and d curve MCBS?
How relay works, reverse relay, master relay, os relay, earth fault relay and what is its setting point
WHAT IS MEANT BY vfd(VARIABLE FREQUENCY DRIVE )HOW CAN WE APPLY VFD TO MOTOR ? I WANT FULL DETAIL IF ANYBODY KNOW THE WEBSITE FOR THAT PLZ SEND .THANK U
how to calculate the surge level of surge suppressors related to the SF6 cicuit breakers?
Why substation battery room is coulered black?
what is %impedanece
what type of earthing is done on hilly rocks.
why only dc is given as excitation...why not ac???
what is stay bow?
In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but what are the other test performed for transformer once it reaches at site.For e.g:if the transformer is dry having rating 1000KVA?