How Can we calculate the rating of a cable?Show the formula?
Answers were Sorted based on User's Feedback
Answer / prof. nazar m. karyar
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit
conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that
represents the direct current resistance for a one thousand
circular mils conductor that is one thousand feet long, at
an operating temperature of 75º C. The direct current
constant value to be used for copper is 12.9 ohms and 21.2
ohms is used for aluminum conductors. The “K” constant is
suitable for alternating current circuits, where the
conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating
current circuits No. 2/0 and larger must be adjusted for the
effects of self-induction (skin effect). The "Q" adjustment
factor is determined by dividing alternating current
resistance as listed in NEC Chapter 9, Table 9, by the
direct current resistance as listed in 2. Feeders – This FPN
recommends that feeder conductors be sized to prevent a
maximum voltage drop of 3%. The maximum total voltage drop
for a combination of both branch circuit and feeder should
not exceed 5%. [215-2(d) FPN No. 2],
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shoebullah
with referance to prof.nazar
answer ... Cant we calculate
voltage drop by this formula
Vd= IZ
where Z= R*cos(pi) + X*sin(pi)
and R= r*1/1000, X=
x*1/1000 ......... I am
suggesting in this way also
we can find voltage drop of a
cable ....... And further we need
to calculate percentage of
voltage drop by this formula
%Vd= sq.root of 3 * Vd/VL
*100
where VL Is line voltage ... It
should be <3% for main
distribution board <5% for all
distribution board
| Is This Answer Correct ? | 0 Yes | 1 No |
what is PPI DB?
2 Answers Priyanka Electricals,
What is the comparision (advantages / disadvantages) of 110V, 60 Hz system to 230 V, 50 Hz system.
Which test will be more severe for VCB?
we have 1000 litre water tank,it located at 25m hight from ground level,the water level on 10m below from ground level.for fill the tank within 1 hour,how much of motor rating(HP) want to select?
Advantages of short circuit and open circuit tests of a transformer?
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
Please explain open transition and closed transistion system in Star delta Starter?and also the state difference of both?
how can we measure the import power and export power in the same line?
415v 14kw so can u tell me how i can measure the cable size.then size of the earth also
what is the id1 & id2 setting in differential protection relay of CSPC?
What is state space method ? Why its used ? Can it applicable on linear, non-linear, 1st order, higher order, homogeneous, non-homogeneous, open-loop , closed loops , stable & unstable systems ?
what is the Auto Mains Failure Panel function in DG?state its function?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)