How Can we calculate the rating of a cable?Show the formula?
Answers were Sorted based on User's Feedback
Answer / prof. nazar m. karyar
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit
conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that
represents the direct current resistance for a one thousand
circular mils conductor that is one thousand feet long, at
an operating temperature of 75º C. The direct current
constant value to be used for copper is 12.9 ohms and 21.2
ohms is used for aluminum conductors. The “K” constant is
suitable for alternating current circuits, where the
conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating
current circuits No. 2/0 and larger must be adjusted for the
effects of self-induction (skin effect). The "Q" adjustment
factor is determined by dividing alternating current
resistance as listed in NEC Chapter 9, Table 9, by the
direct current resistance as listed in 2. Feeders – This FPN
recommends that feeder conductors be sized to prevent a
maximum voltage drop of 3%. The maximum total voltage drop
for a combination of both branch circuit and feeder should
not exceed 5%. [215-2(d) FPN No. 2],
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shoebullah
with referance to prof.nazar
answer ... Cant we calculate
voltage drop by this formula
Vd= IZ
where Z= R*cos(pi) + X*sin(pi)
and R= r*1/1000, X=
x*1/1000 ......... I am
suggesting in this way also
we can find voltage drop of a
cable ....... And further we need
to calculate percentage of
voltage drop by this formula
%Vd= sq.root of 3 * Vd/VL
*100
where VL Is line voltage ... It
should be <3% for main
distribution board <5% for all
distribution board
| Is This Answer Correct ? | 0 Yes | 1 No |
what type of protection and safety req. in the 220kv substaion and area around the substation
how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
what things to be considered when designing UPS
0 Answers Aplab, Veta Kipawa ICT Center,
TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?
What is the meaning of high reputuring in HRC fuse.?
can we say current flows inside an atom as electron moves inside an atom?
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
Moving Iron instruments are applicable with a) DC only b) AC only c) DC & AC
14 Answers Bhel, Engineers India, Engineers India Limited,
what is buscoupler adopter panel????
which type of winding is used for high voltage & low current?
what is the use of vector group in transformer. means what r the application of various vector groups?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)