Answer / prof. nazar m. karyar
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit
conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that
represents the direct current resistance for a one thousand
circular mils conductor that is one thousand feet long, at
an operating temperature of 75º C. The direct current
constant value to be used for copper is 12.9 ohms and 21.2
ohms is used for aluminum conductors. The “K” constant is
suitable for alternating current circuits, where the
conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating
current circuits No. 2/0 and larger must be adjusted for the
effects of self-induction (skin effect). The "Q" adjustment
factor is determined by dividing alternating current
resistance as listed in NEC Chapter 9, Table 9, by the
direct current resistance as listed in 2. Feeders – This FPN
recommends that feeder conductors be sized to prevent a
maximum voltage drop of 3%. The maximum total voltage drop
for a combination of both branch circuit and feeder should
not exceed 5%. [215-2(d) FPN No. 2],
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shoebullah
with referance to prof.nazar
answer ... Cant we calculate
voltage drop by this formula
Vd= IZ
where Z= R*cos(pi) + X*sin(pi)
and R= r*1/1000, X=
x*1/1000 ......... I am
suggesting in this way also
we can find voltage drop of a
cable ....... And further we need
to calculate percentage of
voltage drop by this formula
%Vd= sq.root of 3 * Vd/VL
*100
where VL Is line voltage ... It
should be <3% for main
distribution board <5% for all
distribution board
Is This Answer Correct ? | 0 Yes | 1 No |
For fixed primary voltage how does secondary terminal voltage of a transformer change if the pf of inductive load is raised from 0.7 to 0.9 with load current remaining fixed ?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
why rating of alternator in kva & induction motor in kw
Wat will happen if R-phase of an alternator is connected to B- Phase of AMF panel fed from alternator
how to test an MCB
how instantanious short circuit current is calculated ? its formula.
can you explain the rms value in simple words....
What are the protections for HT Motors?
we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?
what is the function of Choke?
9 Answers Airport Electrical, Cummins, Tamco,
what is the function of potential transformer in s/s