can i know how to design overcurrent setting and earth
fault for 11kv & o.433kv system assuming tx 1000kva.
Answers were Sorted based on User's Feedback
Answer / prakash.
First selected for ct ratio in HT panel.1000kva transformer full load current in primary 52.5amps.so ct ratio in 60amps(60/5).
Now relay setting for over current 55amps.
And earth fault setting 0.5amps in ct secondary amps..
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Normally EFR is set at 20% 0f OCR setting.
Is This Answer Correct ? | 2 Yes | 0 No |
what is isochronous mod? what is voltage drop mode and p.f mode?
america 60hz electric supply is used; but india it is 50hz; why? and if we use 60 hz supply what changeg has to be done or all the equipment has to be thrown which has rating of 50hz frequincy
I have 2 Nos of 2500kVA 33/0.415V cast resin transformers. How to decide on ampere rating of HT Panel? Also advise me how many panel RMG i have to consider whether 4 panel ok?
how did the testing of protection relays done through current injection
Sir 33kva 2 transformer load 900 amp calc 1800 amp mana jayega
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
in which direction real power and reactive power flow and why???????
what is impedence voltage
which type sylbuse involved
what is the purpose of using battery in dg sets, please specify in details.
use of PIR in ehv breaker
1.stranded resistance values of motors? 2.how to calculate the resistance values of single phase and 3phase motors?