Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why generating voltage is limited up to 22kV?

Answers were Sorted based on User's Feedback



Why generating voltage is limited up to 22kV?..

Answer / iamdon

The generating voltage is limited up to 22kV due to
following reasons.

1)At voltage greater than 22kV, it is not ecomomical to
design the insulation for generator.
2)With the increase in voltage,armature current increases
which causes more loss in winding.So temperature of winding
increases which in turn rise the temperature of machine.So
we need more efficient cooling technique which is again
uneconomical.

Techinacal data:

1)5 degree increase in temperature reduces the life of
insulation by a factor of half.
2)20 degree increase in temperature reduces the insulation
resistance by a factor of half.

Is This Answer Correct ?    9 Yes 1 No

Why generating voltage is limited up to 22kV?..

Answer / surendra

1. due to insulation cost.
2. for high voltage generation flux shuld be more for const
freq. thtwhy size of m/c become large which is not
economical.

Is This Answer Correct ?    1 Yes 0 No

Why generating voltage is limited up to 22kV?..

Answer / gurucharan singh

As we go higher voltage level we to provide more insulatio
at generator winding. This increase the normall winding
working temperature indirectly cost of manufacturing.
Further higher temperature reduces life cycle of winding.
It alway preferred to limit generator winding voltage up to
22KV.

Is This Answer Correct ?    0 Yes 0 No

Why generating voltage is limited up to 22kV?..

Answer / s.arul

1) In generator voltage increased as well as increase the
winding insulation thickness.
2) so generator stator core size will be large.
3) In generator size also large.
4) Increase the cost of generator.
5) to transport the generator some problem will come.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Caliculate the Specific Fuel consumption of 320 kva diesel genarator set?

3 Answers   AllTech, RRB,


how one can check the Current of a DC 12 V battery ? Procedure. I told that take a thick wire (having more wires in it) and then join the + and - terminals of battery with the help of two ends of a thick wire .... is this correct or wrong .....

1 Answers  


Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million

2 Answers  


why we connect the capacitor bank in star , not in delta in any system

2 Answers  


in an electronic tri vector meter when the current and voltage sequence changes ? what is the effect of phase sequence on recording of meter

0 Answers   L&T,


what is the minimum recommended leakage current of an earthed cable connected to the body or skid of an alternator

0 Answers  


IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?

4 Answers  


Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?

4 Answers  


when a airgap of the induction motor gets larger does it draw more current ??? does it power factor gets lower?

3 Answers  


What are the Steps for Testing of 20MVA (make:-CGL) Transformer? How many Test we have to do?

2 Answers   BSL,


How we can find the regulation of transformer?

2 Answers  


HOW MUCH MAXIMUM CURRENT TAKEN BY NEAUTRAL IN 125 KVA DG SET

1 Answers   KOC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)