Dear All,
In a 400V power system, ratio of three current transformers
installed incoming switchgear is 4000/1. Maximum three
phases short circuit current of this system is 48kA. One CT
is installed on neutral of upstream transformer (6/0.42kV,
solidly earthed) for 51G protection. Would you please inform
me about the correct CT ratio of this current transformer
(on neutral)??
Thanks a million
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The maximum earth fault current occurs when the phase comes
in contact with the earthed metal part.That will be about
230/0.5 i.e. about 500 A ,ignoring impedance of tr and
taking ER as 0.5 ohms.It is the usual practice to set EFR at
20% of OCR setting.For REFR the CT ratio should be the same
as that of phases.You can have a 2 core 4000:1 NCT and set
the 51G at 0.1 to 0.2 In ,using one of the two secondaries.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Further you can not expect much earth fault current in
neutral earthing as the voltage is only 230.Unless the phase
comes in contact with earthed metal part or welding is done
on the ground, this current will be too low to be picked up
by ct.As the power supply points are provided with fuses
,the relay may not get a chance to act at all.
| Is This Answer Correct ? | 0 Yes | 0 No |
can anyone explain the star-delta motor control wiring ,which wire go where and how they operate?
Why tripping not occur when the transmission lines (11KV & above) breaks? Doesn't we provide earthfault protection for it?
why we use carbon brush in exciter&genrator?
Regarding units, for voltage we are denoting Volts as V but in case of current we are not denoting Ampere as A instead as I..Why..? Any technical reason for this..?
In Single Phase AC Supply,If Voltage between Phase and Neutral is 230V means what will be the Voltage between Phase and Earth?
what is the purpose finding power factor?
How we calculate the size of ht cable for any transformer
In ht capacitor ckt we are using LBS Panel it having isolator with fuse, one of HT fuse flash over, so what is reason behind this event.
HI, I want to buy a new Xformer to my plant. what are the main parameter should I check ( Xformer rating is 16 MVA)
what is phase voltage phase current line current and their usage? provide diagram
How to take of Transformer oil Break down voltage test?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)