Dear All,
In a 400V power system, ratio of three current transformers
installed incoming switchgear is 4000/1. Maximum three
phases short circuit current of this system is 48kA. One CT
is installed on neutral of upstream transformer (6/0.42kV,
solidly earthed) for 51G protection. Would you please inform
me about the correct CT ratio of this current transformer
(on neutral)??
Thanks a million
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The maximum earth fault current occurs when the phase comes
in contact with the earthed metal part.That will be about
230/0.5 i.e. about 500 A ,ignoring impedance of tr and
taking ER as 0.5 ohms.It is the usual practice to set EFR at
20% of OCR setting.For REFR the CT ratio should be the same
as that of phases.You can have a 2 core 4000:1 NCT and set
the 51G at 0.1 to 0.2 In ,using one of the two secondaries.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Further you can not expect much earth fault current in
neutral earthing as the voltage is only 230.Unless the phase
comes in contact with earthed metal part or welding is done
on the ground, this current will be too low to be picked up
by ct.As the power supply points are provided with fuses
,the relay may not get a chance to act at all.
Is This Answer Correct ? | 0 Yes | 0 No |
derive the formula of amp hours is calculated for 12v battery.where no. of plates is given
Sir, I m 3rd year student 4m DCE and want to do internship in siemens or l&t or any other mnc related to electrical engineering. please tell me the procedure 4 same and oblige me
For an 100kw generator, only 50kw of load is connected. Will the generator generate only 50kw or 100kw. If it generate 100kw what happens to rest of the 50kw. What happens if we connect more than 100kw of load?
What is time response of the control system?
What is the material used for the core of a high freiquency transformer?
15 suspects are rounded by the police and questioned about a bank robbery. Only one of them is guilty. The suspects are made to stand in a line and each person declares that the person next to him on his right is guilty. The rightmost person is not questioned. Which of the following possibilities are true? A. All the suspects are lying. B. The leftmost suspect is guilty. B only
why we use 3 phase in our country?..why no 4,5 or 2??
what is meant by auto transformer?
HOW TO TEST A LIGHTENING ARREST ER ?
0 Answers Bhushan Power Steel,
what about the power of wattmeter at starting and loding?
when 20hp 3 phase motor start no load condition in star or delta connection.find current and write formula.(tariq)
Is ground earthing required for neutral conductor of a prime mover ie DG set?