what is difference between power & distrubution
transformer ?
Answers were Sorted based on User's Feedback
Answer / sagar sethi
TRANSFORMERS RATING MORE THAN 1600 kVA ARE COMES UNDER
POWER TRANSFORMERS.
TRANSFORMERS RATING UPTO AND INCLUDING 1600 kVA ARE COMES
UNDER DISTRIBUTION TRANSFORMERS.
THESE ARE SPECIFIED AS PER INDIAN STANDARD 10028 (CODE OF
PRACITICE FOR SELECTION,INSTALLATION AND MAINTENANCE OF
TRANSFORMERS PART-1, PAGE NO-4).
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / ashutosh
Power Transformer Have High KVA ratings As Well As Its Have
Larger In size . In Power Transformer we provides to the
Air Balst Cooling Or ONAN Type Cooling(OIL NATURAL AIR
NATURAL)
While The Transformer Have Less KVA rating As Wll As In It
We Use to The NAtural Air Cooling Or Oil Cooling
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / surendra
power t/f which step down from HV to LV. ratings of the
power t/f is in mw supply is given to this t/f by
generating station or substation. while in the distributon
t/f it step down the suply from 11kv to 440v or 230v. the
supply is directly given to the consumer.
Is This Answer Correct ? | 0 Yes | 1 No |
Questions :- HR- Q.1 about yourself & family background ? Q.2 Why u choose Power sector as ur carrier starting not any other sector ?? Q. 3 What think abt NTPC ? Techincal Questions:- Q.1 about Vocational Training……What u did , see the main equipments….etc Q.2 Why a transformer Noise during its running condition ? Q.3 about transformer oil material & Test name for the measurement of its dielectric strength & wht will u do if its dielectric strength goes low ? ……..some discussion type ? Q.4 What is relation between transmission lines & Communication lines ? Q.5 Which Machine u will prefer to use at a place where flammable gases are coming out & why ? Q.6 how fault in an electric system is detected & hw protection of equipments is done ? Q.7 Why we didn’t feel electric shock in an electric train ?? Q.8 Anything u want to ask from us ??
44 Answers Akona Engineering, Bhel, BSES, Cranex, DRDO, JCB, NTPC,
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
1)why the transformer rating in KVA insted of KW 2)why the secondary of ct is shorted and why the PT secondary is open
if reactive power become zero in transmission system then what effect on system.???
why we ht line cable size small rather than lt cable.
What is meant by Active and reactive power?
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
why the transformer ratings in kva or mva?
what is neutral ground resistance relay? how it is helpful in protecting system?
what is softstarter?
if we use contactor & MCCB both in a feeder.in this feeder rating of contactor is higher or lower or same of MCCB rating & why?
What does the term “voltage regulation” means?