what is LA CT PT panel?
Answers were Sorted based on User's Feedback
Answer / nishad
LA - lightnig arrester: it is use to protect the equpment /
system from dangerous atmospheric lightining.
CT - Current transformer:we can't talk load out put
directly to the meassuring equipmet from the load line. We
use CT for that purpose. It is useing for meassuring the
load current & other meassuring Data( Ampere, KW/KVA, PF
etc).In the cause of protection CT is very essential, such
as over load ( solid state OLR - CT through) Earth fault,
Differetial Protection etc.... WE need CT's servies in Both
LT / HT.
PT - potential transformer:It is also useing for meassuring
the voltage & other meassuring Data( KW/KVA, PF, HZ etc).In
the cause of protection PT is also very essential,such as
under voltage,over voltage, Under HZ, OVER HZ etc... we
can't take the reading directly from the line in cause of
HT so we are usein PT.WE need PT's servies in Both LT / HT.
| Is This Answer Correct ? | 31 Yes | 4 No |
Answer / jariwala vishnu m.
LA - lightnig arrester
CT - Current transformer
PT - potential transformer
the panel from which all the above stated equipment are
controlled is LA CT PT panel.
with the help of this panel we can get data as well as
control the substation's equipment.
| Is This Answer Correct ? | 22 Yes | 6 No |
with the help of this panel we can get data(HT unit
measurement, basiclly for HT use)
| Is This Answer Correct ? | 8 Yes | 8 No |
what is the highest voltage for transmitting electrical power in india
How we select the vector group of 3phase power transformer?
Which of the following can be operated at higher frequencies ? -SCR -MOSFET -IGBT
What is the main use of rotary phase converter ?
What are the RGGVY, APDRP, RE?
phase association of 3PH L&T static CT meter is wrong. means 1PH & 1 CT connected properly and other 2 voltage and CT's inter changed. what would be the impact in the reading?
what is the disadvantage if earth is connected to neutral
is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
Why we transmit the power at the voltage in the multiple of 11 or 1.1 like 11kv, 22kv, 66kv, 132kv...... some one told me that it is due to fomr factor 1.1 of sine wave. its fine but while transforming we can choose any voltage, so why only multiple of 1.1 there also.......? plz tell me.
What is the difference between Generator Differential Relay and Transformer Differential Relay?
Details about Flux Compensated magnetic Amplifer starter for motors
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)