In CDG type IDMTL realy O/L , E/F, O/C which are used for
out going feedrs,on R-phase o/c element, Y-phase , e/f
elecment and on b -phase o/c element will be connected .
Why the earth fault on center phase only, why not on other
two phases?
Answers were Sorted based on User's Feedback
Answer / sathiyaseelan.m
I thing you may misunderstand that.
As per your Qtn.: It has 2 O/c 1E/F
That means Over current b/n R&Y & Y&B so 2 O/c and this two
are eough to protect the Entier system from O/C.
And the earth fault sences from all phases unbalanced load
only. That means Internaly all are taken for refarence
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / gova
This is called 2 O/C+1E/F relay scheme.This scheme is used
mainly where the transformer connection is Dyn11.
please refer the current distribution in this transformer
when a fault occurs in feeder.
This scheme will be sufficient to clear the faulty
section.But nowdays 3O/C+1 E/F relay scheme also used in
many places
gova
Is This Answer Correct ? | 6 Yes | 2 No |
Which motor has high starting torque
How to calculate the current carrying capacity of sized cables, and there is any formula. please send to 'than.achu@yahoo.com'
why neutral should connect to earth in delta-star type transformer
why we need of power factor correction? give advantages
what is power factor when in view of a lineman
What will happen if we give DC supply to AC motor?
what a function diesel generetaor turbo charger & turbo charger is more heated explain reason ?
Why generating voltage is limited up to 22kV?
which motor is used in electric train...???????
what is droop control?
How to decide no. of Step and Kvar for APFC Panel 40 kvar MD: 33.12 KVA Avg pf : 0.8540
whats the differece between Exd and Exe