In CDG type IDMTL realy O/L , E/F, O/C which are used for
out going feedrs,on R-phase o/c element, Y-phase , e/f
elecment and on b -phase o/c element will be connected .
Why the earth fault on center phase only, why not on other
two phases?
Answers were Sorted based on User's Feedback
Answer / sathiyaseelan.m
I thing you may misunderstand that.
As per your Qtn.: It has 2 O/c 1E/F
That means Over current b/n R&Y & Y&B so 2 O/c and this two
are eough to protect the Entier system from O/C.
And the earth fault sences from all phases unbalanced load
only. That means Internaly all are taken for refarence
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / gova
This is called 2 O/C+1E/F relay scheme.This scheme is used
mainly where the transformer connection is Dyn11.
please refer the current distribution in this transformer
when a fault occurs in feeder.
This scheme will be sufficient to clear the faulty
section.But nowdays 3O/C+1 E/F relay scheme also used in
many places
gova
Is This Answer Correct ? | 6 Yes | 2 No |
how to calculate the capacity of CT operated LT trivector meters on a particular distribution transformer.
What is the difference between Earth and Neutral?
IAM GOING TO ERECT THE STREET LIGHT.,, I NEED HOW TO CALCULATE LUX., ILLUMINATION.,AND ALL
what will happen if the field and armature both are made to rotate in a synchronous machine ?
Why electricity is generated and transmitted at the values of multiples of 11?
why synchronous motor has zero starting ?
It is used or not HT cable single core 630 sqmm in LT 3 phase capacitor bank which is used in PCC(power control center).
what is real , reactive and apparani power
why frequency should be constant?
I WOULD LIKE NOW WHY WE CANT USE SOME CT FOR MESARING AND PROTECTION
How out of step protection relay works?
why dc series motor has high starting torque