what is the terminal voltage of dc series generator running
at rated speed at no load?
Answers were Sorted based on User's Feedback
Answer / nithi
we can get only residual voltage across the terminals(due
to residual magnetism).dc series generator cannot build-up
it's voltage without the load.
ONE INTERESTING FACT IS,
DC SERIES MOTOR SHOULD NOT BE STARTED WITHOUT LOAD WHEREAS
DC SERIES GENERATOR CANNOT BE STARTED WITHOUT LOAD.
OK...............
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / senthilkumar
the high should be follow so, the series generator has a
load to run a generator
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
Any body can help me in getting LT panel test procedure.
WHAT IS MVA RATING OF KOTHAGUDAM THERMAL STATION POWER TRANSFORMER?
what is fundamental difference between voltage and current
star delta starter contorl circuit... drawing..
where is highest transmission voltage is used in india
what is the difference b/w low voltage motors & medium voltage motors
why power factor is only cosine angle not sine angle?
what would happen if reactive power (kvar)is increased (more)or decreased (less)? how much exact reactive power should be maintained? and what should be done for that
What is the difference between EXE and EXD
what is stacking factor?
what is the difference between b c d curves on mcb
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)