If Two Generators are working parellel in a network and
suddenly the field of one Generator get weakened What will
happened if there is no reverse power relay fixed in that
Generator panel????
Answers were Sorted based on User's Feedback
Answer / g.bhardwaj
If two generators are working in parallel & no reverse
power relay installed then during weakened of field of any
gen set,definetly sick gen set work as a induction motor &
other gen set trip due to overload.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nishad
If there is no reverse power relay fixed, then it
definetely work as synchronous motor. if it work as the
same, it will affect the present network, because
1, It will draw the current from the other & will trip the
particular network system.
2,Already both generator working in parellel.so if one fail
the full load of the system will be the responsible of
working one. that's why it'll trip by over load.
3, If that field weaked generator work as a motor, it
defenitelt affect the primover ( Diesel Engine / Turbin)
there will be a chance of break down if it don't stop.
IF any another answer pls welcome>>> Nishad
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / lankesh
what you ment by field weakening Assuming field voltage is
reduced and another gen is having enough capacity, the weak
field gen wil deliver less reactive power as the mechanical
energy supplied is not reduced continue to deliver active
power
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Less excitation?. Then the generator will continue share the
load at leading power factor resulting in higher armature
current as the prime mover is still running and the terminal
voltage of the Gen is reduced.If this current exceeds the
set value ,Gen will trip on OCR which does not allow for
very low pf.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.jeyvelraja
The weaked field get another set zero so that particular
gen worked not agenerator
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / raju pohane
if in running condition one generator field wdg became weak
that time this generator will go in field weakening
position and speed will suddenly high and generator will
trip on over speed due to tripping in one generator, load
will shift on another generator and if there will no span
for load in another generator it will also trip.
| Is This Answer Correct ? | 1 Yes | 3 No |
why we are using KVA rating for transformer,not KWh rating?
why DG,Transformer,UPS capacity will be tell in KVA but not in KW?
Electromagnetic torque developed by the motor is compared to shaft torque. A less B same C depends on motor design D more
how ti maintain the power factor in power generation
The initial current is very large at the time of starting for almost all DC motors. SO WE USE STARTER FOR A SAFE STARTING but at our homes we don’t see any starters in our coolers, motors.WHY DON’T WE NEED STARTERS FOR THESE APPLIANCES?
explain the application of reciprocity theorom
What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection
Explain what is electric traction?
what is ballast
What is thermal relay and how it is works in transformer please explain
What is the difference b/w fanuc alpha series 16i and 18i controller. what is stand for i
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)