can we correct the p.f.of ac generator?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Yes.By varying the excitation i.e. the terminal voltage.If
the voltage of the generator is more than the grid
voltage ,the pf will be lagging and the vice versa.But the
pf has to be maintained at 0.9 to 0.98 lag ,for system
stability.A poor pf results in higher armature current
which is also not desirable
Is This Answer Correct ? | 22 Yes | 2 No |
Answer / mohammad afzal
yes, we can correct the p.f of ac generator by manually
varying the volatage of generator and exciting current of
the field rotor. the recommended range of the p.f should
between 0.9 to 0.98 lagging. poor p.f more armature current
and increase in temperature of stator which is not
desirable.
Is This Answer Correct ? | 1 Yes | 0 No |
how we can calculate LT side current of transformer
How to reduce current flowing in neutral due to unbalanced load conditions in a three phase system.
sometimes, eventhough the HV side of the transformer is opened there is a voltage in LV side .How is it possible?
why we dont store the ac power in battery?
whether starting current is limited to rated current of motor through soft starting or it exceeds the rated current?
The shot circuit in any winding of transformer result? Explain
Detailed working of a diesel generator set ?
1 Answers Airtel, Honda, Kirloskar,
what is auto transformer
1. Synchronization is not required A. Thermal B.Hydel C.Wind D.Nuclear
2 Answers APGenco, Birla Power,
what is the procedure for cable sizing or on what basis we will calculate the size of cable?????
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
why do we use magnetic contactors ?circuit breakers are not enough?