i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
Is This Answer Correct ? | 0 Yes | 0 No |
which is the slowest motor? and wt is speed ?
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
why transformer comes only in standard rating like 11kv,33kv,66kv....and not like 33.33kv and so on?
what is difference between KW and KVA
what is ferranti effect?
As all us know that the capacitor panel is connected to improve the power factor when it is PF is low. whether we can connect the capacitor panel on D.G. side(? If it is yes means why?
as per BIS supply voltage in India is ......
why the name trunking bus PT
how we calculate the motor rating of pump for water suction ?its any formula for that plz give thank u
If 110 volts ac is mixed up ith 12 volts dc what will be the resultant voltage and what is the wave form?
WHAT IS THE ANALYSIS OF FREE WHEELING DIODE IN FULL WAVE CONROL RECTIFIER?
I have calculated load for an office building which is 1200 KW as all the load is single phase therefore its 1200 kw single phase. Now i have to design Transformer and Generator for this load Please kindly give me exact answer that how much capacity of Three Phase Transformer and Three Phase Generator is required for this load.