i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
| Is This Answer Correct ? | 0 Yes | 0 No |
What is d diff. btw MCB & MCCB???
how to flameproof electrical motor on the shaft?
What is FM 200?
what is real time system type definition
What is the knee point of voltage of CT?
what is the difference between multimeter and megger?
I have a 380 KVA DG set. How can i find out 1. My Fuel Consumption per hr ? 2. Electricity produced in 1 Hr. ? 3. If load varies then how does it affect fuel consumption & electricity produced ? Please HELP !!! Really need an answer.
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
1 Answers IAG Automation, REL,
When motor stater and roter air gap do big then what will moter.
State kirchoff current law?
Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)