i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
| Is This Answer Correct ? | 0 Yes | 0 No |
What is auto changeover and how it works plz write details.
what are the types of transformers
what is legal process of dg set?
What is the voltage b/w nutral and earth
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
What is Ton Capacity of Air Conditioner?
What is the PI test stand for transformer and what is the producer to do this test?
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
What are all present producing cost of Per KWH of various Fuel?
why neutral of 6.6 kv star connected sq. cage induction motor does not get earthed, though for earth fault protection it is must.
What is EHT(Abrebiation,Function,Voltage Regulation & how it works?
Why should we use jelly filled armoured cables in underground Communication system? What is the use of the Jelly? If we go for unarmoured, then what happens?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)