What is the PI test stand for transformer and what is the
producer to do this test?
Answer / k.prakashchandra
PI means 'polarisation index'.It is the ratio of megger
values at 10 th minute and that at first minute.This value
should be more than 1 and more than 1.5 is preferred.For
this motorised megger is required.For appx value, if you do
not have such megger ,values after 60 seconds and 10
seconds may also be considered.
| Is This Answer Correct ? | 2 Yes | 0 No |
Dear all, is ther any body who can tell me about the setting of ACB(air circuit breaker ). what kind of it,s setting is and how to do it,s setting. also please tell me the setting of VCB(vaccume circuit breaker) . please tell me their setting,s. i will b very thank ful to all of u. Thank,s and Regard,s. Muhammed Ikram.
what is meant by fuzzy logic? what is fuzzification and defuzzification?
give me name of current and volatge control device
why nearly all voltages are in the multiples of 11?
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
what happen when dc supply is given to the transformer
What is differnce b/w tie breaker and bus coupler?
what is the minimum requirement gigaohms for the insulation test using 5kv in 300mm xlpe cable
DG B-check,C-Check,D-check is depending upon the running hrs.If the running hrs is not reached as mentioned.How to conduct the DG checks.
What is the difference between switch gear and control gear ?
kva/kvr
why ohmas low not sutable to transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)