Answer / ramji
The differential protection is used for protecting the
transformer from internal winding fault,internal winding
shorts etc.,.It operates through three sets of CT's
connected in and out of transformer.It may or may not
operate during minor earth faults.REF is used to detect the
earth fault at restricted zone where its protection CT is
connected.It will surely operate during earth fault.But not
in windings short.
Is This Answer Correct ? | 31 Yes | 4 No |
Answer / gunasekaran
both are using for internal fault but differential
protection only sensitive up to 92% winding of the
transformer if any fault occur in balance 8% winding diff is
not operating so we r using REF protection
Is This Answer Correct ? | 11 Yes | 7 No |
Answer / nikhil thakkar
REF and Differential both pritection are for internal zone and SEF for external zone. Actual all protections are voltage/current/power based and they are back to each other. DIFFERENTIAL AND REF both protection is for internal fault i.e trafo winding . differential sense unbalance between both end of trafo. /Gen. . REF sense unbalance caused between NCT and phase CTdue to earth fault abd actual backup for REF is SEF.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashish
as per my knowledge ref protections hav to be assigned
separately on both sides of traffo it protects 90% of
winding.
it is unit protection and its very sensitive.
while talking about diff protection two cts in each phase
on both sides of trafo is there any diff in incoming and
outgoing current will leads to trip so both are equally
required.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / raveendra nath
Differential protection provides excellent protection for
phase- to-phase and most phase - to - earth faults, this
element is less sensitive for single- phase-to-earth faults
close to the earth point in solidly earthed transformers.
For these faults (i.e fault at transformer winding turns
nearer to neutral point ), phase current changes very
little, but large current flows in the neutral.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / gunasekaran
at internal earth fault condition diffrentional sensitive
only 85% only remaining 15% covered by REF protection
Is This Answer Correct ? | 1 Yes | 8 No |
Answer / munish
REF 64T is used for protect the 95% winding of T/F.it sens
only the internal fault of T/F and 51NT circulating earth
fault relay used for detect the other area.
87T diff. is act only when the difference B/W both side
current is more than setting value
Is This Answer Correct ? | 0 Yes | 8 No |
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
how to produsing geretor power
tan delta test of current transformer.
Why Transformer Neutral having one earth pit ( more earth electrode resistance) whereas body have many earth pit ( less earth electrode resistance)?
what is the constructional difference between a power transformer and potentian transformer?
what is the maintain in ACB,VCB,MCB,MCCB breakers?
What will be MF for below rating ? Main CT PT value is 11kva/110 and 20/5 amp Meter display is 1kva/110v and -/5 amp What will be MF ? Multiplycity factor of energy meter
what is the relation between the leading pf and supply voltage?
For a 500 MVA 400/220/33KV transformer following data given HV power = 500 MVA IV power = 500 MVA LV power = 5 MVA If input power is 500 MVA then how output power is (500+5)MVA. Can anyone help
if HT side voltage is high current is low . and LT side voltage is low current is high please explian.
what is the load amp for 1 HP 3 phase Motor ?
What are the basic elements used for modeling mechanical translational system?