If I have a motor of 1 MW with 6.6 kV, running at 35% load,
how can I save energy without reducing the load?
Answers were Sorted based on User's Feedback
Answer / mohammad a.monem salama abu se
BY REDUCING THE FREQUENCY
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
You can not lower the load ,capacity, and voltage. To save
energy ,you are left with only reduction of line current to
lessen the I^2R losses.The pf of motor is highest at
full ,or nearly full load.At 35% load ,the pf is less and
hence, the line current is more than required to take the
load (HP)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / maheshbabu calicut
by installing VFD(variable frequency drive)we can vary the speed of induction motors.at 35%load you can run the motor at low speed hence saving power
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Replace the motor with one of lower rating.
Is This Answer Correct ? | 1 Yes | 1 No |
How to reduce current flowing in neutral due to unbalanced load conditions in a three phase system.
what is the funtion of conservator in transformers?
why DC is not generated instead of AC?
Just a silly question but just to make my curious mind bac to normal - Why was not 67 and 67N relays built into a single relay as i have noticed that the R,Y,B CT wiring end up into the 67 relay while the common of the R,Y,B CT wiring end up into the 67N relay. Then it was better if a single relay was manufactured just like the distance relay (21). Another question i would like to ask is - how do we know where the 67 and 67 N relay has to be placed.why is it not placed at the transformer bay? In the substaion that i am working -i have noticed that it is placed between a breaker and a common double bus bar and this line bay is connected to another substation at a remote place which is furthur connected to a load. B U S______CT for 67 & 67N ______Breaker _____ remot s/s. B A R
Can a 5 core cable one end with a 32A 3p+N+E plug and the other end 32A 3p+E be used on a generator?
what is pressure relief valve?where it is used????
what is the total power generation in india?
Sir, why generating power plant operating at above 0.9 lag? detail explaination?
why ELCB can't work if N input of ELCB do not connect to ground?
what percent do you derate your copper wire when you change from copper buss to copper wire
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
what are the industrail measures to overcome ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system? plz reply