why we use REF and Differential Protection in one
transformers?my doubt is both protections are operated in
internal fault only.why we want to use 2 protections?please
clarify.
Answer Posted / munish
REF 64T is used for protect the 95% winding of T/F.it sens
only the internal fault of T/F and 51NT circulating earth
fault relay used for detect the other area.
87T diff. is act only when the difference B/W both side
current is more than setting value
| Is This Answer Correct ? | 0 Yes | 8 No |
Post New Answer View All Answers
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
Is there a standard depth of gravel fill in Substation Switchyard? Please give a design/drawing. Thank you.
Whether 3 phase induction motorwith 100 hp capacity , Amp 160 for which sensitive earth fault relay , type CTUM 15 can be used?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
WHY SEPARATELY EXCITED MACHINE NEEDS EXCITATION BY DC SUPPLY WHY NOT BY AC
How 3 phase invertor works?
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
How much pf maintan in dg set in 6o% load,when Dg runnig Neutaal Earthing removed what happen.
what is the concept of directional power?
What is the formula for calculating no-load current?
how we calculate electrical load on a building according to area?
can anyone please help me to find the rupturing or breaking capacity in KA of circuit breaker (MCCB,VCB,ACB etc) of HT and LT side of a distribution transformer...please help with detailed step by step answer...thank you
WHAT IS THE DIFFERENCE BETWEEN AN ACB & mccb 7 WHAT IS THE CRITERIA WHEN TO USE WHICH OF THE TWO
give some advantages and disadvantages of combiniing the session, presentation, and application layer in the osi model into one single application layer in the internet model
If the earth is a good conductor of electricity, why don't people get shocked every time they walking on earth?