Answer / santosh kawade
Following protections are used for feeders below 132KV:
1) Over current protection (normal inverse and
instateneous),
2) Earth fault protection (Normal inverse curve),
3) Horm 4 protection (feeder protection),
santosh kawade
9224 69 3116
| Is This Answer Correct ? | 37 Yes | 4 No |
Answer / rama krishna. inampudi
1) Over Current prptection
2) Earth Fault protection
3) Distance protection
| Is This Answer Correct ? | 23 Yes | 2 No |
Answer / narayana reddy
1) Over Current prptection
2) Earth Fault protection
3) Distance protection
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / p.mahesh goud
1.over current protection
2.earth falth protection
3.Distance protection
4.shart circuit protection
| Is This Answer Correct ? | 4 Yes | 0 No |
WHAT WILL HAPPEN WHEN THE MOTOR FREQUENCY INCREASED OVER THE RATED MOTOR RPM THROUGH DRIVE?
what is the need of starter in tube light and what type of starter is used in that?
Is there any rule to select the voltage of motor based on KW rating? What is the rating above which lt motor becomes the HT motor?.
1.what is bus cuplour and main funtions. 2.what is main function of alternator. 3.how many types of dg oils.
What is the diff. between two phase & three phase supply.
What is corona? and what is the purpose of corona belt in substation ? why they connect these end of the buses ?
what is a switchgear. what is its work & where it is used?
Why 36 KV LA is used in 33 KV Line and 9 KV LA is Used in 11 KV Line
1 Answers APTransco, Bhel, Wipro,
what is The difference between national electrical code and I.S.Code (electrical) and what is the value of NEC in electrical engineering field
for testing busbar (33kv) hi-pot .whether we can apply DC r not.and what is the test volt for that .explain
Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?
we all know that in transformer, voltage and current are inversely related i.e. Vp/Vs= Is/Ip....so in standard CT..we have a ratio of 200/5...that means our voltage should increase by ratio of 40..althoug that is not the case...because that requires high insulation level.and pratically not feasible......can anybody clarify my ques.......thanx
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)