Recently we had experienced following problem
All RCCB breakers (connected to the load as well as spares)
connected to various UPS systems at various floors at a
high rise building tripped during a power break down and
upon starting up of generator.This Generator is recently
inducted into the installation. Can any one explain the
reason behind this tripping.
Regards
Viswanathan
Answer / k.prakashchandra
If it was the first time for the gen, then wrong leads to
the bus-bars is suspected.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the disaddvantages of high power factor
explain me the exact concept of generator neutral....????
can i connect REF and Differencial relay in 1 CT core for transformer protection?
What is the need for checking knee point voltage for CT's?
Dry type transformers
what is disadvantages of high power factor
In hydel power plants, L.A's, S.C's are placed inside the control panel boards. what is the purpose? [already the total body was earthed to ground.]
what is the difference between core & shell type transformer ?& where we use those transformers ?
What is the function of Harmonics filter, and how to calculate that rating of the energy saving?
How can we get electric power from lighting ?
Should power factor be low or high?
I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)