how to select a breaker (MCB,MCCB,ELCB) for 18.5 kw, 3 ph.
480 v, 60 hz induction motor?
Answers were Sorted based on User's Feedback
Answer / engr ali mehmood
MCB are used for small power application; usually used in
the household appliances current rating is 5A.
MCCB are used in high power application in generation
station above 100A;Rarely used but the most common used in
industries is MPCB variable Rating of current adjust
according to the load current of the the appliances. and
the ELCB is a earth leakige circuit breaker it is use for a
body earth ground earth
| Is This Answer Correct ? | 27 Yes | 18 No |
Answer / simon peter
Here 18.5w means 480v*38 amp so buy any one of these impere based ......
| Is This Answer Correct ? | 4 Yes | 7 No |
Answer / jayaraj
P=Sq rt 3VI pf
So I = 27.8 Amps. considering the staring current twice as full load current = 55A so 63 A MCCB required. Depends on the KA of the system 25KA or 50 KA MCCB can be selected.
| Is This Answer Correct ? | 13 Yes | 17 No |
Answer / s.k.sharma
MCB are used for small power application; usually used in the household appliances current rating is 5A.
MCCB are used in high power application in generation station above 100A;Rarely used but the most common used in industries is MPCB variable Rating of current adjust according to the load current of the the appliances. don't know about the ELCB just cheak out on Wikipedia...
| Is This Answer Correct ? | 10 Yes | 22 No |
How much sq,mm cable need for 800 amps load
How we calculate the Multiplying Factor of Kwh meter for 3 phase alternator.
What is the difference between Welding Transformer and Normal Transformer?.
directional over current relay when acted & how it works
how to calculate of which rating transformer should be selected? take any example
does a DG set has low fault level as compared to that of a transformer.If yes then why.
What is the relation of current with torque when motor started in Y-connection???
cable tray sizing & selection
What are the different condition monitoring techniques for a motor?
HOW WE KNOW IN PHYSICALLY THE CONTACT SURFACE OF A VACUUM INTERRUPTER IS GOOD OR GOING TO DAMAGE IN A VCB AFTER ABOVE 500 TIMES OPERATED.
what r the earthing required for commissioning of D.G set?
What causal system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)