can we charge 3 ph power transformer delta-star wound with
neutral grounded 6.6kV/415V from secondary side(415V) but
with primary(6.6kV) open by dg,what are the disadvantages or
losses.
Answer / k.prakashchandra
Yes .But when you use 6.6 KV side ,you will lose earth fault
protection.There will not be any difference in losses
Is This Answer Correct ? | 0 Yes | 0 No |
inductive power factor is benefit compare to capacitive????
how to find transformation ratio of squirrel cage induction motor
what exactly commisioning work does in electrical site work... LT side?..
Does the total power means fundamental plus Harmonics?
Though transformer consist winding which usually cause reactive power change in both generator and motor but it wont affect reactive power passing through transformer why?
what happen if we give 220 volts dc supply to d bulb r tube light?
what is the principle of operation of CFL ??
What is mean by spike arrester(Voltage Operated)
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
How i can decide that HVDC line is best for transmission.
how the capacitance is caluclated if the load is varying to keep the power factor constant(above0.95)
How many types of interlocking use in screw type air compressor,make-Kaser(BSD MODEL)?
0 Answers Automobile, Siddhi Vinayak,