For polarity test on a 11/3.3kV 2.5MVA delta-star Unit
Auxiliary transformer,415V 3-phase supply was applied at
the HV. Connection between Aa was made with a 2.5mm cable.
As soon as power was switched on the cable caught fire and
burnt. This test was then abandoned. It is noteworthy to
say that a similar cable was also used in a similar
transformer for the same. The cable did not burn and test
was successfully completed with good result. What is wrong?
Please, help me out.
Answers were Sorted based on User's Feedback
Answer / jatinder singh
Please do the megger testing of HV winding.May be the
winding was short circuited.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurucharan singh
When cable burnt, it is clear that there was over current
in the 2.5mm2 cable. That means load connected may faulty,
or oversize then the capacity of 2.5mm2 cable current
carrying.
| Is This Answer Correct ? | 1 Yes | 1 No |
Thanks to the respondent.I would like to tell him that no
load was connected besides linking Aa in accordance with
the method for the test. Also, note that similar 2.5mm2
cable has been used on a similar Unit Auxiliary 2.5MVA
11/3.3kV delta-star T/F and 60MVA 132/11kV star-delta T/F
respectively. No burning occurred. Test results were
satisfactory. This piece of information should guide any
contributor. Thanks.
| Is This Answer Correct ? | 0 Yes | 0 No |
why we used servo motor insted of inducation motor?
difference between substation & grid substation?
what is impedence in transformer
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
Explain What will happen when direction of field current is changed (i.e, field excitation is reversed) in the following machines? 1) Alternator 2) Synchronous Motor 3) D.C Generator ( Shunt or Seies ) 4) D.C Motor ( Shunt or Seies )
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT
how we can check new PT ? without name plate.
1 Answers Indo Power Projects,
why voltage between neutral and earth, with out secondary grounded distribution transformer
What is the different between digital phase converter and ordinary phase converter?
how much winding resistance of 0.75kw to 12.5kw 3ph sqwiralcage induction motor?
what is protections used for 6.6kv ht motor
What is a soft start?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)