Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


For polarity test on a 11/3.3kV 2.5MVA delta-star Unit
Auxiliary transformer,415V 3-phase supply was applied at
the HV. Connection between Aa was made with a 2.5mm cable.
As soon as power was switched on the cable caught fire and
burnt. This test was then abandoned. It is noteworthy to
say that a similar cable was also used in a similar
transformer for the same. The cable did not burn and test
was successfully completed with good result. What is wrong?
Please, help me out.

Answers were Sorted based on User's Feedback



For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply w..

Answer / jatinder singh

Please do the megger testing of HV winding.May be the
winding was short circuited.

Is This Answer Correct ?    1 Yes 0 No

For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply w..

Answer / gurucharan singh

When cable burnt, it is clear that there was over current
in the 2.5mm2 cable. That means load connected may faulty,
or oversize then the capacity of 2.5mm2 cable current
carrying.

Is This Answer Correct ?    1 Yes 1 No

For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply w..

Answer / engr. l. o. osuji

Thanks to the respondent.I would like to tell him that no
load was connected besides linking Aa in accordance with
the method for the test. Also, note that similar 2.5mm2
cable has been used on a similar Unit Auxiliary 2.5MVA
11/3.3kV delta-star T/F and 60MVA 132/11kV star-delta T/F
respectively. No burning occurred. Test results were
satisfactory. This piece of information should guide any
contributor. Thanks.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.

0 Answers   Allied Group,


what is EBXl (electron beam cross linked ) cable ?

1 Answers   Polycab,


The loads are connected with phase and ground then why current flow as the loads ?

0 Answers  


I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.

0 Answers  


what is the working of air compressor.

5 Answers  


How to address the servo drive for motor

0 Answers  


Why AC & DC capacitor are use in UPS ??????????????????

0 Answers   Sanghi,


how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor

0 Answers  


what is the difference between CT and CVT in EHV Sub Stations

4 Answers   Hofincons, Lanco, TATA,


How to test Power Transfomer vector group in the field?

3 Answers   Al-Yamama,


Pls tell me whether we can use EN3A material for shafts of Permanent magnet alternator.What will be the effect of magnetic and nonmagnetic material for shafts on magnetic properties of PM rotor .

0 Answers  


Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)