For polarity test on a 11/3.3kV 2.5MVA delta-star Unit
Auxiliary transformer,415V 3-phase supply was applied at
the HV. Connection between Aa was made with a 2.5mm cable.
As soon as power was switched on the cable caught fire and
burnt. This test was then abandoned. It is noteworthy to
say that a similar cable was also used in a similar
transformer for the same. The cable did not burn and test
was successfully completed with good result. What is wrong?
Please, help me out.
Answers were Sorted based on User's Feedback
Answer / jatinder singh
Please do the megger testing of HV winding.May be the
winding was short circuited.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurucharan singh
When cable burnt, it is clear that there was over current
in the 2.5mm2 cable. That means load connected may faulty,
or oversize then the capacity of 2.5mm2 cable current
carrying.
| Is This Answer Correct ? | 1 Yes | 1 No |
Thanks to the respondent.I would like to tell him that no
load was connected besides linking Aa in accordance with
the method for the test. Also, note that similar 2.5mm2
cable has been used on a similar Unit Auxiliary 2.5MVA
11/3.3kV delta-star T/F and 60MVA 132/11kV star-delta T/F
respectively. No burning occurred. Test results were
satisfactory. This piece of information should guide any
contributor. Thanks.
| Is This Answer Correct ? | 0 Yes | 0 No |
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
what is EBXl (electron beam cross linked ) cable ?
The loads are connected with phase and ground then why current flow as the loads ?
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
what is the working of air compressor.
How to address the servo drive for motor
Why AC & DC capacitor are use in UPS ??????????????????
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
what is the difference between CT and CVT in EHV Sub Stations
4 Answers Hofincons, Lanco, TATA,
How to test Power Transfomer vector group in the field?
Pls tell me whether we can use EN3A material for shafts of Permanent magnet alternator.What will be the effect of magnetic and nonmagnetic material for shafts on magnetic properties of PM rotor .
Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)