For polarity test on a 11/3.3kV 2.5MVA delta-star Unit
Auxiliary transformer,415V 3-phase supply was applied at
the HV. Connection between Aa was made with a 2.5mm cable.
As soon as power was switched on the cable caught fire and
burnt. This test was then abandoned. It is noteworthy to
say that a similar cable was also used in a similar
transformer for the same. The cable did not burn and test
was successfully completed with good result. What is wrong?
Please, help me out.
Answers were Sorted based on User's Feedback
Answer / jatinder singh
Please do the megger testing of HV winding.May be the
winding was short circuited.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurucharan singh
When cable burnt, it is clear that there was over current
in the 2.5mm2 cable. That means load connected may faulty,
or oversize then the capacity of 2.5mm2 cable current
carrying.
| Is This Answer Correct ? | 1 Yes | 1 No |
Thanks to the respondent.I would like to tell him that no
load was connected besides linking Aa in accordance with
the method for the test. Also, note that similar 2.5mm2
cable has been used on a similar Unit Auxiliary 2.5MVA
11/3.3kV delta-star T/F and 60MVA 132/11kV star-delta T/F
respectively. No burning occurred. Test results were
satisfactory. This piece of information should guide any
contributor. Thanks.
| Is This Answer Correct ? | 0 Yes | 0 No |
Does the total power means fundamental plus Harmonics?
When i went to a interview the interviewer ask me a question for that i cant able to answer him if anyone knows answer me How will you design a capacitor bank for a plant? if my p.f is 0.6 i have to improve it to 0.9 or 1 what kind of steps i have to do? and is there any formula for calculating this?
what is the impedence
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
Are same transformer be employed for step up and step down services?
What are the conditions to be satisfied before connecting two DC generators in parallel?
3 phase Motor will be given 2 phase after 2 to 5 second we given 3rd phase so Motor Run sum-time in forward or sum time run reverse direction. All time phase sequence is not change. Why motor run in reverse direction? Please Explain........
explain the process of commutation in a dc machine. Explain what are inter-poles and why they are required in a dc machine.
why we need the starters for motors
What is the capacitance values of 132,220,400 & 765 kV current transformer
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
can u please mail me the syllabus for GET exam for damodar valley corporation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)