what is the effect of power factor in electrical circuit ?
if we mainten power factor near about unity (0.999) our
energy consumption Units increase or decrease?
Answers were Sorted based on User's Feedback
Answer / yogesh
As we know Load is in KW & it is constant. PF will not
change units consumed as we are measuring energy consumption
units in KW not in KVA, only transmission losses will be
reduced.
KW=1.73 X V X I X cos phi
AS KW is constant, voltage is constant if cos phi changes
current will be changed.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / b chaudhary
Power facotor does not effect on energy consumption.But
transmission and distribution losses can be reduced.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rahul verma
Electrical energy is exclusively
generated,transmitted,distributed in the form of
alternating current.therefore the question of power factor
immediately comes in to picture.since most of the loads are
inductive in nature hence have low lagging pf.low pf is
highly undesirable as it causes increase in current,and
additional losses of active power in all the elements from
power station generation till the utilization devices.
if we maintain pf as close to unityour consumption unit
decrease
| Is This Answer Correct ? | 13 Yes | 8 No |
with power factor at unity the power consumption will not
get effected . but for sure the production cost will
decrease with which the cost of consumption will decrease.
and how the production cost will decrease???
answer is with unity pf the real power will be v*i*cos@=v*i
which is actuall input power and now is usefull power.
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / santosh kawade
Electrical energy is exclusively
generated,transmitted,distributed in the form of
alternating current.therefore the question of power factor
immediately comes in to picture.since most of the loads are
inductive in nature hence have low lagging pf.low pf is
highly undesirable as it causes increase in current,and
additional losses of active power in all the elements from
power station generation till the utilization devices.
If we maintain pf as close to unity transmission losses
reduces but our consumption units will not change.
santosh kawade
9224693116
| Is This Answer Correct ? | 3 Yes | 1 No |
if power factor lagging then losses will increase, then more
units will consumption.pf should not in leading position.so
to reduce that losses we ll maintain pf close to unity....if
pf is 1 then we ll get kva=kw....reading...THEN UNITS WILL
GET REDUCE,....
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sumedh chaccravorty
The units consumed will NOT change but the company might( most probably will) impose punishments for operating at lower PF as it increases the transmission losses and increases the KVA rating of the associated devices.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / parasuram
effect of power factor in eleectrical circuit is if power
factor is very less reactive power wwill be more it will
cause to damage circuit and energy consumption units
increase.
if power factor is near to unity it will decrease the enegy
cosumption units.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / suraj ojha
As per power fourmula :-
1.Unit cosumption will raise for consumer.
2.Unit generation will increase for genarating station.
| Is This Answer Correct ? | 1 Yes | 5 No |
which pump used in STP
explain the process of commutation in a dc machine. Explain what are inter-poles and why they are required in a dc machine.
What is the difference between Analogue Addressable Systems and intelligent Addressable Systems
what is stray loss in transformer?
We operate a 10 Mw facility and we have been experiencing several trips due to fluctuations on the MVAR? We have checked all issues related to the AVR and we have found all OK? Can anyone help us? The grid voltage, internal voltage, all regular parameters look ok. MVAR fluctuate and there it goes the unit? What could be happening? Thanks!
what is the difference b/w winding insulation class and winding temperature class?
What is C-factor?why it is required to consider in fault short circuit calculations?
what is the temperature rise test? explain in brief.with formula.
WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR
why does same amount of current flow in the circuit inspite of any number of resistances in the circuit?
what is the use of earthing ?
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)