what is the effect of power factor in electrical circuit ?
if we mainten power factor near about unity (0.999) our
energy consumption Units increase or decrease?
Answers were Sorted based on User's Feedback
Answer / yogesh
As we know Load is in KW & it is constant. PF will not
change units consumed as we are measuring energy consumption
units in KW not in KVA, only transmission losses will be
reduced.
KW=1.73 X V X I X cos phi
AS KW is constant, voltage is constant if cos phi changes
current will be changed.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / b chaudhary
Power facotor does not effect on energy consumption.But
transmission and distribution losses can be reduced.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rahul verma
Electrical energy is exclusively
generated,transmitted,distributed in the form of
alternating current.therefore the question of power factor
immediately comes in to picture.since most of the loads are
inductive in nature hence have low lagging pf.low pf is
highly undesirable as it causes increase in current,and
additional losses of active power in all the elements from
power station generation till the utilization devices.
if we maintain pf as close to unityour consumption unit
decrease
Is This Answer Correct ? | 13 Yes | 8 No |
with power factor at unity the power consumption will not
get effected . but for sure the production cost will
decrease with which the cost of consumption will decrease.
and how the production cost will decrease???
answer is with unity pf the real power will be v*i*cos@=v*i
which is actuall input power and now is usefull power.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / santosh kawade
Electrical energy is exclusively
generated,transmitted,distributed in the form of
alternating current.therefore the question of power factor
immediately comes in to picture.since most of the loads are
inductive in nature hence have low lagging pf.low pf is
highly undesirable as it causes increase in current,and
additional losses of active power in all the elements from
power station generation till the utilization devices.
If we maintain pf as close to unity transmission losses
reduces but our consumption units will not change.
santosh kawade
9224693116
Is This Answer Correct ? | 3 Yes | 1 No |
if power factor lagging then losses will increase, then more
units will consumption.pf should not in leading position.so
to reduce that losses we ll maintain pf close to unity....if
pf is 1 then we ll get kva=kw....reading...THEN UNITS WILL
GET REDUCE,....
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sumedh chaccravorty
The units consumed will NOT change but the company might( most probably will) impose punishments for operating at lower PF as it increases the transmission losses and increases the KVA rating of the associated devices.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / parasuram
effect of power factor in eleectrical circuit is if power
factor is very less reactive power wwill be more it will
cause to damage circuit and energy consumption units
increase.
if power factor is near to unity it will decrease the enegy
cosumption units.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / suraj ojha
As per power fourmula :-
1.Unit cosumption will raise for consumer.
2.Unit generation will increase for genarating station.
Is This Answer Correct ? | 1 Yes | 5 No |
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
why buchholz relay is kept on inclined position and why it is cover??
If carbon brushes spring tension either loose or tight, what happen on Motor performance During Full load Operation?
how can we calculate fault current of a line in a 6 bus syatem if the faulted line is known?
why there is a humming noise in transformer
Why reactors use before incoming of ac vvfd drive?
how "rabbit ACSR" conductors are more efficient than "weasel ACSR" conductors
How to calculate the TR (AC's)
what is the diffrence between resistive load and capoasitive load.?
what is meant by transformer?
why would the rotor rotate at sub synchronous speed against the direction of rotating flux when d rotor of 3 phase IM is connected to 3 phase balanced supply and the stator windings are shortcircuited ??
what is the different between rms and average value