Why the generating station rating is in KW though the
rating of generators in KVA?
Answers were Sorted based on User's Feedback
Answer / vittal
generating station main aim is to meet the load which can
be met completlely by the mechanical units or the source of
the prime over ,which must be mention in kw.
where as the rotationg ac machines are rated in kva
because of the losses ie the iron and copper (not on pf)
mention in kva
but even the pf is also mention on the alternator which
means the generator should be operated on that load
ex: if rating of the plant is 100 then if alternator of 0.8
pf is selected the rating of the generator must be 125
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / satya
though generators rating in kva ,but station rating must be
in kw . because we have to exlpress the output power interms
of true power
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / jaggannath swami
All the loadd received by any generators is known by kilowatt i.e. kw bcose its a source of power . whoich I calculated in terms of kw The equipment rating is shown by kva & its depends upon the calculation whatever we used
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m.pushparaj
in generating station power is not based on the power
factor but the generator based upon the connecting
load,that is apparent power.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / electrical testing engineer
Generators are also rated in KVA. In our general terms we use terms 30KW machine but actually technical rating of any generator is in KVA.
All equipment which can supply the power are rated in KVA, because their O/P power will depend on the load type you connect with it. 45 MVA machine can give as high as 36 MW power if you improve the PF or other machines are pumping enough reactive power in the network. Thus generator Watt will vary depending on the load same as the transformers. transformers too can operate on varying degree of the MW loads depending on the load connected.
Only electrical loads such as motor, heaters are mentioned in KW.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rakesh
generater rating is in kw becoz losses in generator mainly
depends on voltage and current and not on nature of load....
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / gopal lal
bcoz of he load type is not fixed for any generation plant
Load to be depended in requirment of the client and
production of the plants.So dont rating KW of the any
generation plants.
Is This Answer Correct ? | 1 Yes | 5 No |
which is the most common harmonics 3rd,5th,7th affect the systegm
How does the phase sequence controller works, how it identifies the phases? confirm working principle
why transformer rating is mentioned in kva?
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
From what on-site components does the HT panel monitoring the bus-bars in a 11kV system take inputs?
WHAT IS THE DIFFRENCE BETWEEN EARTHED AND UNEARTHED CABLE (XLPE)?
deisel generators all elcetical calculation formule's
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
according to ohms law ,the voltage increases then current is what happened?
why we short ckt the secondry vo5tage/ winding in transfr and motor?
WHICH IS BETTER( FOR POWER SAVING)- ON LINE OR OFF LINE UPS ?
3 Answers Punjab National Bank,
why we are using star connection and delta connection? difference?