how to measure the dc current?
Answers were Sorted based on User's Feedback
Answer / manoj sharma
We can easily measure AC currents by AC ammeters as AC
currents can be stepdown by current transformer and 0-1 A
current can easily be measured by ammeters. But in case of
DC current it can not be step down. For this a shunt (A
high resistance in parallel of the sorce) is used to reduce
the dc current. As you already know the source voltage,
I=V/R, this will give current through the resistane. at the
same time you knoe resistance of the wire in which high DC
current is flowing. V1=V2(In parallel arrangement)hence
I1=V2/R1. now Ammeter can be calibrated to show the current
R2/R1 times of it.Where R2 is the shunt resistance and R1
is lead resistance across which ammeter and shunt are
installed.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / avd
DE current is measured through shunt. Shunt is a standered
low resistance. It is used in series in the circuit. Due to
series circuit, load current flows through shunt. Because
of this there will be a millivolt drop across the shunt
(ofcource depending on the current). This millivolt drop
across the shunt is measured and meter is calibrated in
terms of current.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mr.sharif
The simplest way to measure DC current is by using DC
ClampMeter/Multimeter.
| Is This Answer Correct ? | 2 Yes | 2 No |
What is function for Load Bank test and why need to test.
What are the disadvantages of hydropower?
how external lighting design? please give examples?
What is the criteria in selecting Air circuit breaker(ACB) & Moulded case circuit breaker(MCCB) for a particular range?
How Self works in DG set
where we take earth in hill station
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
Does power factor vary with speed?If yes, how?If not, why?
In dc motor starter there is less voltage required for holding contactor that's may why it is called no volt coil. but in ac starter why holding contactor is called no volt coil.
what is meant by phase transformation ratio in induction motors?
which type of motor is suitable for water suction pump ?
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)