why we have to do tan delta test of the transformer oil???
Answers were Sorted based on User's Feedback
Answer / chinni
Tan delta test is test for measuring the insulating
capacity of transformer oil.The value of Tan delta deals
with the leakege current through Insulating oil.
| Is This Answer Correct ? | 23 Yes | 4 No |
Answer / vels
to determaine the insulation condition if the tan delta
value is higher than 0.7 for a transformer,then oil has to
be tested in all aspects .from the oil results we can under
stand where the insultion is weaks
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / sunil guru
tan DELTA test is used to determine the insulation strength of oil
to determine the break down strength,flash point,its fire point,and also to identify the moisture content of the oil
their is certain fix value for all above said......
if the oil colour changes then it may be said that it may not be suitable for large time......
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / tapan desai
Know about insulation
degradation of transformer
and power cable.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / pati
Ionic traces can effect the Tan delta of insulating oil
like transformer oil.The amount of charge particle directly
proportional to the electrical properties, hence tan-delta
test essencial for Transformer oil.
| Is This Answer Correct ? | 3 Yes | 3 No |
What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?
what will happen if the bus PT fuses are accidently removed from the circuit in 6.6kV feeder?
what is basic difference between the normal tube light choke and electionic choke ?
what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??
is it possible to minimize the copper loss?
which is the most common harmonics 3rd,5th,7th affect the systegm
what is reluctance?
I want to know what is the short circuit level when 8 NOS 2000 kVA, 415v, 50hZ generator connected in paraller
Why used in layer by layer charcoal and salt used in earth pits.
11 Answers CESC, HP,
Megar test tell sufficient resistant
what is the resultant phase shift in a 3 phase power system including neutral if on or more phases gets grounded or short circuited. kindly explain in detail for the reasons...
I know the Capacitor value- 12.5KVAR, voltage 440V gas filled, then what is the formula for calculate the microfarad value for this 12.5KVAR capacitor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)