I want to know what is the short circuit level when 8 NOS
2000 kVA, 415v, 50hZ generator connected in paraller
Answer / s c budhiraja
Taking 10% impedence of one gen.the faut level of one gen
will be 16000kva or 2.8KA at 415 Volts.the faut level for
eight generators will be 2.8x8=22.4KA
| Is This Answer Correct ? | 2 Yes | 4 No |
when neutral will carry the current?what could be the magnitude?
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
What is the normal phase difference between the voltage and the no-load current in a transformer?
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for grounding? 3)What is the difference between ELCB &RCCB? 4)Why we use iron core in transformer insted of wooden core? 5)what is the principle of excitation? 6)Why we test the core balance test for transformer? 7)what is creepage?What is the creepage length for insulators at different voltages? 8)How much type of relays used for differential protection of generator,transformer & busbar protection?
Is this possible to synchronize the two different ratings of dg
how we can check that any motor is faulty may be single phase or three phase?
in general it is observed in power stations, the tertiary winding is used in higher rating Y-Y auto transformer but not in Y-Y power transformer. is the tertiary winding is compulsory then why it is not using in power transformer
What is the percentage loss for aluminium wire for HT line more than 11KVa
Why do power lines not short out when they fall into water?
Is there thumb rule to calculate how many Insulators to be used for Transmission line of different volatges
how to reduce the initial starting amps which is equal to the running load amps
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)