I want to know what is the short circuit level when 8 NOS
2000 kVA, 415v, 50hZ generator connected in paraller
Answer / s c budhiraja
Taking 10% impedence of one gen.the faut level of one gen
will be 16000kva or 2.8KA at 415 Volts.the faut level for
eight generators will be 2.8x8=22.4KA
| Is This Answer Correct ? | 2 Yes | 4 No |
what is the function of choke and starter in a tube light??
What is the rating of HT SUBSTATION and LT SUBSTATION?
How many methods use the load flow solution?
Why Powers are named in MW?
what is the standard duration after failure EB power
what is ATS & RING MAIN UNIT in Distribution System?And its Function.
IAM WORKING IN THERMAL POWER PLANT AS A TRAINEE.. I WANT TO IMPROVE MY CARRIER., IF ANYBODY KNOWS ANY COURSES., ANY TESTS, ANY BOOKS ,, ANYTHING PLS HELP ME..
Suppose the incoming power is 11 kw, but the load require only 8 kw means how can we save or use the excess power?
design of IGBT firing circuit for 11KV
Are same transformer be employed for step up and step down services?
all electricals questions
What difference between ref protection and differential protection ?
0 Answers EPC, INEL Power System Engineers,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)