I want to know what is the short circuit level when 8 NOS
2000 kVA, 415v, 50hZ generator connected in paraller
Answer / s c budhiraja
Taking 10% impedence of one gen.the faut level of one gen
will be 16000kva or 2.8KA at 415 Volts.the faut level for
eight generators will be 2.8x8=22.4KA
Is This Answer Correct ? | 2 Yes | 4 No |
How can we choose the rating of submersible motors
How to calculate the volumetric capacity of a oxygen & Nitrogen gas Cylinder if pressure is 145 kg/cm2 & water capacity of cylinder is 67 liters.
what is the problem in manufacturing transformer with 0 degree phase displacement.???why alwasys go for DYn11 or DY5?Whys not DY0 i.e zero degree displacement between primary and secondary side vectors?
3 Answers Bhel, dpdc, Prime Electrical,
What will happen if i used 11KV earth ht kit to 11 KV / 11 KV cable termination?
What is the basic difference among IPS,UPS,EPS?
WHY THE +VE POLARITY OF 48V DC POWER SUPPLY IS USUALLY GROUNDED?
in 3 phase induction motor resistance value is how much
why the admittance matrix or y bus matrix of a large network is called sparse matrix?
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
WHAT IS INERTIA,AND WAT IS TORQUE.
what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.
why rating of generator is kva but motor is kw ?