Why we use Y-Y connection in power transformer (8-10 MVA,
132 kV to 11 KV)and D-y in distribution transformer (2 MVA,
11 KV to 440 Volts)?
Answers were Sorted based on User's Feedback
Answer / rajesh kumar
we use y-y conection in exctra high voltage transformer
like 132kv as we know that in star connection line voltage
is-1.732.phase voltage.so less insulation required in y-y
conection.
in distrubution transformer at 11kv we can easily insulate
windings due to voltage level is low.and also get domestic
load.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rajesh kumar
we use y-y connection in power transformer 132kv as we know
that in star connection line voltage is-1.732.phase
voltage.so it is easy to insulate the winding as the
voltage level is low.and cost is less due to degrading of
insulation.
| Is This Answer Correct ? | 3 Yes | 0 No |
ok u r using any transformer , anywhere but
the important is what is ur need ?
if u want , in distribution u need 440v -phase to neutral
u r using star connection
u need 11kv hv , u use delta connection
the important is u r using neutral or not generally line
side transformer has delta connected
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / morongoa
WE USE Y-Y CONNECTION IN POWER TRANSFORMER COS WE NEED STAR
POINT SO IN DELTA YOU DNT HAVE A STAR POINT AND FOR
DISTRIBUTION YOU USE D-Y CO YOU TAKING POWER FRM SUBSTATION
WHICH IS 11KV FRM SUB TRANSFORMER TO YOUR CONSUMERS
| Is This Answer Correct ? | 1 Yes | 8 No |
A synchronous machines has higher capacity for (1) Leading power factor (2) Lagging power factor (3) Does not depend upon the power factor of machine (4) None of the above
how to calculate the ct burden?
Explain how you intend to work under pressure to meet up with deadline target?
What is the Relation b/w star delta starter , DOL starter and two speed starter. if we want to rotate a 20 kw fan in 2 speeds which type of two speed starter we have 2 use?
Initially motor starts with star connection ,after few timing changes to delta connection, why the motor should run continously in star connection,it gives high torque & low current?
how can we test the vector group of transformer
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
MICOM P122 OC/EF RELAY HAVE HARMONIC RESTRAIN OR NOT?
who is make controlling in the reactive power that genarted in AS genrator(the exitaion currnt or exitation voltge)
when two gen set runing in parallel but thay have diffrent pole pitch, then what will be happan
Transformer not operated in dc ! why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)