What is the Relation b/w star delta starter , DOL starter and
two speed starter.
if we want to rotate a 20 kw fan in 2 speeds which type of two
speed starter we have 2 use?
All the starters you have mentioned is for starting and
running the motor. DOL starters are usually used for smaller
motors where the starting current will not affect the
distribution system or the motor itself or the connected
machine, wheres star delta starters are used for bigger
motors and where the winding terminals are available for
such starting, whereas the two speed starter can be only
used if you have a motor with two speed windings.
If your 20kw motor comes with two speed termination than you
can use the two speed starter if not than you may use
inverters where by selecting the frequency you may vary the
speed of the 20kw motor
| Is This Answer Correct ? | 4 Yes | 0 No |
How the speed of synchronous motor changes with the variation of load?
When can we take Neutral as common neutral link?
highest rating of alternator used in india
what is the distance b/w EHV lines? 1.8m 2.11m 3.4m 4.14m
how the harmonics are generated in transforemer?
1.What is captive power plant? 2.What is national grid?Give brief idea.
why motor rating in KW?
What is the meaning of transformer 16 / 20 mva.
What is Creepage distance?
what is Diversity factor in electrical installations
difference between local breaker backup relay or backup protection relay ?
How to calculate HV Cable Sizing & what are the factors to be considered for selection?.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)