WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO
MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE
THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR
VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?

Answers were Sorted based on User's Feedback



WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF Y..

Answer / jyotirmaya

Thanx a lot for your reply.
Kindly post the minimum accepted IR value.

Is This Answer Correct ?    4 Yes 2 No

WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF Y..

Answer / rajavelu

ir value test
33kv,66kv,220kv

Is This Answer Correct ?    3 Yes 1 No

WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF Y..

Answer / yash

yes.megger test is prformed and IR value is almost 1G Ohm

Is This Answer Correct ?    1 Yes 0 No

WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF Y..

Answer / amji r jadhav

the megger test ir is infnt 0 your ans but 33kv line charge in the stand by minimum 10mgo this is the megger value

Is This Answer Correct ?    0 Yes 0 No

WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF Y..

Answer / krupa

Megger Test is applied on surge Arrestors and its accepted
IR Value is infinity

Is This Answer Correct ?    5 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

diff b/w normal grounding and resistance grounding

0 Answers  


define as synchronous generator

0 Answers   Enercon,


how to calculate the torque of a motor?

0 Answers  


What is the difference between Class PX & Class X CT's

2 Answers   ABB,


why the air gap is necessary in the transformer core

1 Answers   Eskom,






What happens when the field of an alternator connected to infinite bus is suddenly removed?

3 Answers  


why fuse amperes rating are specified ratings like 32amp & 64 amps?

2 Answers  


3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.

0 Answers  


How many safety of Disel Generator

5 Answers   Sail,


How to use earthing on shipments.

0 Answers  


For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?

0 Answers  


why are transformer rating in MVA

2 Answers   Suzlon,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)