For KVA rating,
The formula for determine the current is:
I = KVA/(1.732 x Voltage) (For three phase system)
I = KVA/Voltage (For Single Phase)
For KW rating
The Formula for current is
I= KW/(1.732 x Voltage x Power factor)(for three phase system)
I = KW/(Voltage X Power factor)(For Single Phase)
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / j.l. singh
If there is three phase system formula for the
KW = 1000.root3 VA cos Phi.
KVA = 1000 VA
V =Voltage A = Ampere.
| Is This Answer Correct ? | 19 Yes | 7 No |
Answer / denzel101
For KVA rating, the formuler for current will be:
I = KVA/(0.707 x Voltage) for three phase system
For KW rating
I= KW/(0.707 x Voltage x cos phi)
for three phase system
| Is This Answer Correct ? | 5 Yes | 17 No |
I have a 600VA UPS for computer only. It holds for 20minutes only. 1. Can it be upgraded for longer period.? 2. Can it be used for one ceiling fan and a tube light? If yes, how to upgrade?
what is the HT motor current setting (Motor protection relay)aganist FLA If the capacitor is connected in parallal to the motor to increase the P.F from 0.89 to 0.99. the setting is to be reduced. what is the formula for to calculate the current.(FLA - CALCULATED CURRENT!= )
what formula can be apply to calculate the No of rtrand of a cable. ?
what is difference b/w squirrel cage rotor and wound rotor
what is the difference between normal motor and flame proof motor??
what is different between relay and plc?
we are using three transformer 33000/430 vac for three separet block.all three transformer have three LT panel separetly. can be Interconnected all three panel through bus coupler. this is permissable or not by state electricity board.
bsnl tta exam question
what the Microsoft .NET framework is?
if we convert kw into Ampers,which one formula use by us,pls tell me?
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
When in a large power system if the demand of power is larger than the generated power the frequency of the power system drops.(assume the rated frequency is 50Hz and now it is 49Hz) So does this mean the demand is totally supplied with a lower value of generated power in a lower frequency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)