Answer / binosh
pressure transmitter:
in bench calibration connect a power supply 24v.give a
250ohms as loop resistance.connect a multimeter in
milliamph mode and connect it in series.and put a
communicator across the loop.the transmitters HP&LP sides
should be in open to atmosphere.this condition the
ammeter shows 4ma and the communicator shows LRV .connect a
pressure calibrator to the HP side and LP keep it open to
atm.apply pressure as the range and go on as 25%,50%,75%and
URV.then the ammeter shows 4,8,12,16,20ma
respectivly.incase you are not getting zero,make zero trim.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / s. kanniyappan
TEMPERATURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT MULTIMETER IN SERIES WITH -VE TO THE TXT
GIVE RESISTANCE INPUT TO THE TRANSMITTER
GIVE LRV VALUE BY ADJUSTING THE DRB
ADJUST ZERO FOR LRV
GIVE URV VALUE BY ADJUSTING THE DRB
ADJUST SPAN FOR URV
GIVE 25%, 50%, 75%, 100% OF URV (RESISTANCE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
PRESSURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT 250 OHMS IN SERIES WITH -VE TO THE TXT
CONNECT THE HART TO THE TERMINALS OF RESISTANCE
CONNECT THE TRANSMITTER TO THE SOURCE VIA REGULATOR AND MAKE
A T OFF CONNECT TO A MASTER GAUGE
VARY THE PRESSURE BY ADJUSTING THE REGULATOR
MAKE ZERO TRIM FOR ZERO PRESSURE THROUGH HART
ADJUST THE REGULATOR AND CHECK FOR THE LRV VALUE IF NOT
MATCHING ADJUST THE ZERO
DO THE SAME FOR THE URV
GIVE 25%, 50%, 75%, 100% OF URV (PRESSURE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
DP TYPE TRANSMITTER
LP LINE SHOULD BE LEFT OPEN TO ATMOSPHERE
CONNECT THE HP LINE TO THE SOURCE AND DO THE SAME AS ABOVE
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar
Any Txr has input, output, supply. give the simulated input
ie.. mA source or mV or pneumatic and check the o/p. if o/p
doesn't match adjust zero or span . Have details of range of
measurements in hand. In need use them also to get desired
output
| Is This Answer Correct ? | 6 Yes | 8 No |
is motorized valve closed when power shutoff?
Explain , how timer based pneumatic control valve will work ?
Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?
How 2 calibrate level tank having large height..?
why we are using digital signals for I/O & how to measure this signals is getting or not ?
Can anyone send most commonley asked Instrumentation questions and answers in cement industry please?
what is cold loop? difference between hot and cold loop?
can we control operation of PLC from operator station?
need instrumentation job completed 1 year trainee ship in mnc pesticide company. now in search of job
How can I read the electrical drawing easily?
what is the difference between Feedback controller and Feed forward controller. and when it is to be used.
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)