Answer / binosh
pressure transmitter:
in bench calibration connect a power supply 24v.give a
250ohms as loop resistance.connect a multimeter in
milliamph mode and connect it in series.and put a
communicator across the loop.the transmitters HP&LP sides
should be in open to atmosphere.this condition the
ammeter shows 4ma and the communicator shows LRV .connect a
pressure calibrator to the HP side and LP keep it open to
atm.apply pressure as the range and go on as 25%,50%,75%and
URV.then the ammeter shows 4,8,12,16,20ma
respectivly.incase you are not getting zero,make zero trim.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / s. kanniyappan
TEMPERATURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT MULTIMETER IN SERIES WITH -VE TO THE TXT
GIVE RESISTANCE INPUT TO THE TRANSMITTER
GIVE LRV VALUE BY ADJUSTING THE DRB
ADJUST ZERO FOR LRV
GIVE URV VALUE BY ADJUSTING THE DRB
ADJUST SPAN FOR URV
GIVE 25%, 50%, 75%, 100% OF URV (RESISTANCE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
PRESSURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT 250 OHMS IN SERIES WITH -VE TO THE TXT
CONNECT THE HART TO THE TERMINALS OF RESISTANCE
CONNECT THE TRANSMITTER TO THE SOURCE VIA REGULATOR AND MAKE
A T OFF CONNECT TO A MASTER GAUGE
VARY THE PRESSURE BY ADJUSTING THE REGULATOR
MAKE ZERO TRIM FOR ZERO PRESSURE THROUGH HART
ADJUST THE REGULATOR AND CHECK FOR THE LRV VALUE IF NOT
MATCHING ADJUST THE ZERO
DO THE SAME FOR THE URV
GIVE 25%, 50%, 75%, 100% OF URV (PRESSURE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
DP TYPE TRANSMITTER
LP LINE SHOULD BE LEFT OPEN TO ATMOSPHERE
CONNECT THE HP LINE TO THE SOURCE AND DO THE SAME AS ABOVE
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar
Any Txr has input, output, supply. give the simulated input
ie.. mA source or mV or pneumatic and check the o/p. if o/p
doesn't match adjust zero or span . Have details of range of
measurements in hand. In need use them also to get desired
output
| Is This Answer Correct ? | 6 Yes | 8 No |
What is output of Thermocouple at 25 deg c
what do you mean by cathodic protection?
line up procedure for dp type flow transmitter?
what is the electrical operation procedure for switching on 27.6MVA electric furnace.
types of valves
3 Answers Bindal Papers, Kuwait Oil Company,
why flow transmitter showing 2.2ma?
what is ment by PID controllers? explain with example?
How an rtd work, and what volts/current goes to a rtd to measure the resistance?
how we use the positioner feed back in split range control valves?
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
I need circuit for RTD senser?
ORP sensor working principle?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)