how to calibrate transmitter
Answers were Sorted based on User's Feedback
Answer / binosh
pressure transmitter:
in bench calibration connect a power supply 24v.give a
250ohms as loop resistance.connect a multimeter in
milliamph mode and connect it in series.and put a
communicator across the loop.the transmitters HP&LP sides
should be in open to atmosphere.this condition the
ammeter shows 4ma and the communicator shows LRV .connect a
pressure calibrator to the HP side and LP keep it open to
atm.apply pressure as the range and go on as 25%,50%,75%and
URV.then the ammeter shows 4,8,12,16,20ma
respectivly.incase you are not getting zero,make zero trim.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / s. kanniyappan
TEMPERATURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT MULTIMETER IN SERIES WITH -VE TO THE TXT
GIVE RESISTANCE INPUT TO THE TRANSMITTER
GIVE LRV VALUE BY ADJUSTING THE DRB
ADJUST ZERO FOR LRV
GIVE URV VALUE BY ADJUSTING THE DRB
ADJUST SPAN FOR URV
GIVE 25%, 50%, 75%, 100% OF URV (RESISTANCE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
PRESSURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT 250 OHMS IN SERIES WITH -VE TO THE TXT
CONNECT THE HART TO THE TERMINALS OF RESISTANCE
CONNECT THE TRANSMITTER TO THE SOURCE VIA REGULATOR AND MAKE
A T OFF CONNECT TO A MASTER GAUGE
VARY THE PRESSURE BY ADJUSTING THE REGULATOR
MAKE ZERO TRIM FOR ZERO PRESSURE THROUGH HART
ADJUST THE REGULATOR AND CHECK FOR THE LRV VALUE IF NOT
MATCHING ADJUST THE ZERO
DO THE SAME FOR THE URV
GIVE 25%, 50%, 75%, 100% OF URV (PRESSURE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
DP TYPE TRANSMITTER
LP LINE SHOULD BE LEFT OPEN TO ATMOSPHERE
CONNECT THE HP LINE TO THE SOURCE AND DO THE SAME AS ABOVE
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar
Any Txr has input, output, supply. give the simulated input
ie.. mA source or mV or pneumatic and check the o/p. if o/p
doesn't match adjust zero or span . Have details of range of
measurements in hand. In need use them also to get desired
output
Is This Answer Correct ? | 6 Yes | 8 No |
Make Heater Process Logic.
how many type conductivity sensor ?
instrumentation
plz give me the logic for how a pushbuttoon can be worked as atoggle switch i m working with allenbradely/micrologix1200/rslogix500
What should we do when Fisher Fieldvue DVC2000 give some out put air at 4mA bt at that i need no out put
How many problems can be occurring in solenoid valve? And how it can be rectified?
i want to know for good instrument engineer or success how many software knowledage required & from which university
Why we use 4 - 20 ma?
use of split range ? where it is used ? in which control loop it is used ?
How to control flow variations in magnetic flow maters..... When i will provide proper earthing?
If we interchange HP and LP tapping in drum level measurement and reverse LRV & URV correspondingly.What is the difference between the normal tapping(HP,LP) and reversed tapping(LP,HP)?
What is the Relation Between flow and pressure. How both terms related with each other.