Answer / salah
Dyn11-secondary voltage lags primary by 30degree
Dyn1-secondary voltage leads primary by 30deg
hence it is not satisfying the condition for
pare;;alisation .
if we connect two TR in parallel current drwn form the
source by both transformer is not in phase hence
circulating current will produce & damage the winding as
well in secondary aslo
| Is This Answer Correct ? | 38 Yes | 13 No |
Answer / tanesh
When DYn11 and DYn1 are out of phase by 60deg. Although the magnitude of both transformers are same, but phase different would cause potential difference between the transformers. This will cause short circuit the two transformers are paralleled.
| Is This Answer Correct ? | 4 Yes | 3 No |
Doug - you are absolutely right for Dyn1. To look at this graphically, a positive 30 degree angle of secondary to primary means that secondary voltage sinusoidal wave starts 30 degrees after the primary sinusoidal wave. Hence in reality it is indeed lagging the primary. Just reverse for Dyn11.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / doug marshall
As I understand it, the convention is counterclockwise
rotation. Therefore DYn1 means that the secondary lags the
primary by 30 degrees (Subtractive Polarity). DYn11 means
that the secondary lags the primary by 330 degrees which is
the same as secondary leads the primary by 30 degrees
(Additive Polarity). Likewise, a DYn1 when operated as a
YnD1 (Step Up), the secondary or delta leads the primary Y
by 30 degrees. Therefore two DYn1 transformers connected in
series DYn1 - DYn1, the output will lag the input by 60
degrees but YnD1 - DYn1, the first stage results in the
intermediate voltage (Delta) leads by 30 degrees and at the
last stage, there is a 30 degrees lagging phase shift so
the sum phase shift from Y - Y is 0 degrees.
| Is This Answer Correct ? | 7 Yes | 17 No |
what is the difference between isolation and insolation ? please explain in detail with example.
what is the electrical?
wich type of cable is selected for wiring of 20hp motor?
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
Why temperature rise test is conducted in bus bars and Isolators?
specific gravity of a battery?
How the flights will be fly be fly without ground connection under raining with thunder lighting?
what is the unit of electricity????????????
what is surge voltage and surge current?
wht factor are considered to design ACB( air Circuit reaker) 415V
why we choose 50 or 60 hertz not other value for the power system?
400kw, 3.3Kv motor want to fix 1000km away from substation. What is full load current? and what is the cable size for motor? I amp expecting answer and advice from your side.. thanks...
4 Answers Kuwait Oil Company, Weatherford,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)