Answer / deepak24
1. SCT and OCT are performed to determine Copper and Iron Loss respectively. so by obtaining these values we can obtain efficiency as follows-
efficiency = input/(input+losses)
2. efficiency can be found for any desired load without connecting it to full load.
3. power consumption is less as compare to full load test.
| Is This Answer Correct ? | 43 Yes | 12 No |
Answer / binayak dey
In the open circuit test as the high internal resistance voltmeter is connected to the high voltage side and the low voltage side is loaded so the current flowing through the low voltage side is determined by the connected ammeter.so the copper loss is neglected and the power loss will also be neglected. So the power factor is minimise and hence the risk factor is minimum.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / hassan
Open circuit test : Finding (Core losses) Rc & Xm.
,Finding Voltage with on load.
Short circuit test:Finding Equivalent (Resistance of windings & leakages flux) .
| Is This Answer Correct ? | 4 Yes | 1 No |
what is difference between earth fault& restricted earth fault.
Why we use ups battery and dsdb battery in thermal power plant
How much water ( Kilo Liters) a submercible pump of 35 HP can lift from Borewell of 6" and 900 feet dip.
Draw torque - speed curve and load curve of induction motor? mark operating point ?
What is ht lt switchgear.
3 Answers Bhel, HBL Power Systems,
What is the full form of AND,OR and other logic gates
operation of protection relay watchdog contact?
What is the difference between Zero Current Transformer and Core Balance CT ?
What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?
If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?
2 Answers Aditya Birla, Siemens,
what will be the effect if you were using different brands of outlets?
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)